  • Sep 29, 2008, 07:15 AM
    Scottyp
    Fan won't turn off
    Installed a new Honeywell Programmable Thermostat RTH7500 for heat pump energy savings. Replaced an old York thermostat "York T874R 1046" with a Honeywell subbase Q674L 1272. After the installed the system worked well with the new thermostat for a few days. Then, I noticed the fan would not shutoff. The fan runs with all settings: System on/off, termostat on/off, and when thermostat is removed from subbase. All connections are solid and no wires are touching.

    My York Air Handler has emergency electrical heat and located in the attic. I do not have an electrical schematic for the unit and a drawing is not mounted inside of the door panel. I think the Air Handler Model is 2HL06501506C (maybe the Coil Model number). Inspected the wiring from the thermostat: all connected, none touching, no visiable problems.

    Im not very AC knowledgeable but not a novice and very comfortable working on the unit and its circuits.

    Any ideas of the cause and test that I can perform.
  • Sep 29, 2008, 09:13 AM
    Scottyp

    Update:
    Thermostat: York/Honeywell T874R1046, sub-base Q674L 1272
    Furnace: York Electric.
    Air handling section: N2AHD14A06
    Heater section: 2HL06501506C

    Where can I find an Electrical Diagram for the York Air Handler unit?
  • Sep 29, 2008, 01:59 PM
    hvac1000
    Look on the inside of the blower door.
  • Sep 29, 2008, 04:28 PM
    Scottyp
    Where is the relay or sequencer?

    Here's a picture of my wiring inside the furnice:
    http://i266.photobucket.com/albums/i...p/DSC04314.jpg

    Here's the inside of the cabinet pictures:
    http://i266.photobucket.com/albums/i...p/DSC04316.jpg
    http://i266.photobucket.com/albums/i...p/DSC04317.jpg
    http://i266.photobucket.com/albums/i...p/DSC04318.jpg
    http://i266.photobucket.com/albums/i...p/DSC04319.jpg


    Where is the relay or sequencer?
  • Sep 30, 2008, 09:53 AM
    Scottyp

    Thanks, I found the diagram inside of the circuit cabinet door.

    I just need a little help here please...
    Where is the relay & sequencer?
    How do you test them?
  • Sep 30, 2008, 10:12 AM
    hvac1000
    Second pic sequencer is on right side. Test to see if M1 and M2 are closed. IE remove power and wires and test across terminals. (REMEMBER WHERE THE WIRES WERE)If they are closed then the sequencer is calling for the motor to be on at all times and it is defective. OR easier test is to just remove wires off M1 (TAPE THEM TO PREVENT SHORT)and energize the unit. If the motor has stopped running the sequencer is locked on and is defective.
  • Sep 30, 2008, 10:45 AM
    Scottyp

    Thanks for a response hvac1000.

    In the second picture, how many sequencers are present? Only one has the M1 & M2 stamp.

    Also in the second picture on bottom left, is a white box. It has what appears to be a switch on the other side. The switch is frozen on one side and will not toggle/reset. What is it?
  • Sep 30, 2008, 05:21 PM
    EPMiller
    Quote:

    Originally Posted by Scottyp View Post
    Thanks for a response hvac1000.

    In the second picture, how many sequencers are present? Only one has the M1 & M2 stamp.

    Also in the second picture on bottom left, is a white box. It has what appears to be a switch on the other side. The switch is frozen on one side and will not toggle/reset. What is it?

    There are 2 sequencers in that picture. Usually those control the electric resistance heat. There usually is another relay somewhere that controls the fan. Your picture is fuzzy, but I wonder if that bakelite brown piece to the left of the sequencers isn't the relay you want. Trace the wiring back from the fan and see if it goes to that piece. If it is, just pull the fan wire off the terminal, turn the power back on (you did kill the juice first, right?) and see if your fan isn't off. If it is, you found your relay. Next reconnect that terminal and pull one of the relay coil leads off. If your fan is still on then replace the relay. Unless something else is in parallel with it, like an overheat limit switch or the like, then you have to isolate the problem to the particular part. You have to use the schematic if you really want to troubleshoot things.

    That white box looks to me (again fuzzy) like a circuit breaker. Those toggles don't move unless they are tripped.

    EPM
  • Sep 30, 2008, 06:40 PM
    hvac1000
    M1=motor one
    M2=motor two.

    Underwriters Laboratories requires a
    fan interlock circuit to insure the blower
    remains operating whenever more than one
    sequencer is used. The fan interlock should
    be the M contacts of the second or third sequencer.






    All M contacts are wired to the blower motor


    so that any sequencer that is energized at will operate blower



    http://www.white-rodgers.com/wrdhom/.../0037-4799.pdf

    http://www.white-rodgers.com/wrdhom/..._06_pg0096.pdf

    Some units have relays and some just use the sequencers
  • Oct 1, 2008, 02:07 PM
    Scottyp
    Quote:

    Originally Posted by hvac1000 View Post
    OR easier test is to just remove wires off M1 (TAPE THEM TO PREVENT SHORT)and energize the unit. If the motor has stopped running the sequencer is locked on and is defective.

    Did the Easier Test. Removed & taped both wires off M1 and turned on the unit.
    Results: Fan came on...


    Quote:

    Originally Posted by EPMiller View Post
    Your picture is fuzzy, but I wonder if that bakelite brown piece to the left of the sequencers isn't the relay you want. Trace the wiring back from the fan and see if it goes to that piece. If it is, just pull the fan wire off the terminal, turn the power back on (you did kill the juice first, right?) and see if your fan isn't off.

    The bakelite brown piece is a relay. I traced a wire back to the fan and disconnected it...
    Results: Fan came on...

    Quote:

    Originally Posted by EPMiller View Post
    If it is, you found your relay. Next reconnect that terminal and pull one of the relay coil leads off. If your fan is still on then replace the relay. Unless something else is in parallel with it, like an overheat limit switch or the like, then you have to isolate the problem to the particular part. You have to use the schematic if you really want to troubleshoot things.

    Pulled one of the relay coil leads..
    Results: No fans but constant hummmm...

    Tested for 24volts on the green wire from thermostat with power on/fan running. Nothing...
  • Oct 1, 2008, 05:45 PM
    EPMiller
    Quote:

    Originally Posted by Scottyp View Post
    <snip>
    The bakelite brown piece is a relay. I traced a wire back to the fan and disconnected it...
    Results: Fan came on....
    Pulled one of the relay coil leads..
    Results: No fans but constant hummmm...

    Tested for 24volts on the green wire from thermostat with power on/fan running. Nothing...

    I'll admit, troubleshooting by email is a lot harder than hands on.

    When you pulled the fan relay coil lead possibly you heard a hum that is always there, just masked by the fan noise. If the fan quit when that lead was pulled, something is energizing the fan relay. I don't know how you tested for 24 volts, but measuring from green to red at the tstat would show 0vac when the fan is being called. That's equivalent to measuring from hot to hot. Green to the C terminal should be 24vac with the fan being called. It appears by your pictures that you do not have an integrated control board so you should be able to trace where that signal is coming from. Turn the tsat so that it is NOT calling for cool (or heat), turn the fan switch to auto, wait for two minutes or so (fan overrun time SHOULD be finished) and then, if the fan is still running, check for voltage between red and green at the tstat. If you still have nothing (0vac) then something is likely wrong with the tstat. Disconnect the green at the tstat, if fan stays running then something is wrong in the wiring.

    I REALLY need that schematic.

    EPM
  • Oct 1, 2008, 07:28 PM
    Scottyp

    Here's the Schematic:
    http://i266.photobucket.com/albums/i...mp/Diagram.jpg
  • Oct 1, 2008, 07:38 PM
    Scottyp
    Quote:

    Originally Posted by EPMiller View Post
    I'll admit, troubleshooting by email is a lot harder than hands on.

    When you pulled the fan relay coil lead possibly you heard a hum that is always there, just masked by the fan noise. If the fan quit when that lead was pulled, something is energizing the fan relay. I don't know how you tested for 24 volts, but measuring from green to red at the tstat would show 0vac when the fan is being called. That's equivalent to measuring from hot to hot. Green to the C terminal should be 24vac with the fan being called. It appears by your pictures that you do not have an integrated control board so you should be able to trace where that signal is coming from. Turn the tsat so that it is NOT calling for cool (or heat), turn the fan switch to auto, wait for two minutes or so (fan overrun time SHOULD be finished) and then, if the fan is still running, check for voltage between red and green at the tstat. If you still have nothing (0vac) then something is likely wrong with the tstat. Disconnect the green at the tstat, if fan stays running then something is wrong in the wiring.

    I REALLY need that schematic.

    EPM

    Agreed... Hands on is a lot better.. But now, I only have a humm... :(
    Fan has stopped running.. :mad:

    Tested for 24 volts from Green to C and thermostat turned off (fan auto). Result 0 volts
    Maybe the relay completely died when testing... Hopefully... :confused:
  • Oct 1, 2008, 07:42 PM
    MarkwithaK

    With your stat off, FAN set on Auto you won't have voltage from G (Fan) to C (Common). Set the Fan to ON and you SHOULD have 24 volts.
  • Oct 1, 2008, 08:02 PM
    Scottyp

    Agreed.. The problem is that I have a fan running continuously with 0 volts on Green (fan) wire... And I don't want it to stay on with the AUTO setting... It SHOULD go off with heat/ac quits..
  • Oct 1, 2008, 10:40 PM
    hvac1000
    Look at 2R (Relay for blower motor) on your wiring diagram (lower right side). If this relay is defective (shorted closed) it will keep the blower running all the time no mater what you disconnect except the main power. Check 2R I have a feeling your problem might be located there.
  • Oct 2, 2008, 06:08 PM
    MarkwithaK

    Some times these relays can stick. You may be able to tap on it to free it up.
  • Oct 2, 2008, 06:31 PM
    Scottyp

    Tapping on the Relay didn't work.. I think it made it worse.. :(
    I went from fan ON always to humming always... :mad:

    Tried to find a replacement blower relay today and can't find one locally. The York (024-24984-000) relay is a 5-pin relay and all of the stores has 6-pin relays. Im being told that it's a (special order only) York part. Im searching online for alternatives..

    Relay Manufactured by: ESSEX
    Essex Part number: 134-20103-301Q
    York Part number: 024-24984-000
    12FLA 60LRA 125VAC
    8FLA 48LRA 250VAC
    18A 277VAC
    COIL 24V 50/60Hz

    Anyone knows of an equivalent relay that I can use?
    What's a good online site for HVAC parts?
  • Oct 2, 2008, 07:03 PM
    hvac1000
    That is just a single pole single throw/single pole normally open relay. Known as SPST/SPNO relay with a 24 volt coil.

    SEE actual page 115 on below info and tell me if it looks something like the relay pictured.

    http://www.white-rodgers.com/wrdhom/...ers_relays.pdf

    If so you will need a 90-370 5 tab unless York had it modified for there usage. BTW you can use a 5 or 6 tab relay. Just follow the wiring diagrams listed on the Whire Rodgers relay page. You just have to used the same numbers for the connections you need. QUESTION?? Is this relay on a circuit board or freestanding?

    Do not worry about the last 000 in the York part number. This site has it but it is expensive there.

    http://bestbuyheatingandaircondition...ory_Code=r-rbm


    Cheaper here at Grainger

    http://www.grainger.com/Grainger/wwg...=19&submit.y=1

    ALSO I would suggest you look on the side of the relay for a wiring diagram and make sure you get the correct one. It will make life easier for you as far as wiring goes. Grainger stocks all these type of relays.

    Here is the list page

    http://www.grainger.com/Grainger/wwg...e&CatPage=3827
  • Oct 3, 2008, 08:13 AM
    Scottyp

    The really at bestbuy Heating & Air Conditioning is the exact match to my relay.
    I do not have a circuit board and the blower relay is freestanding.
    Its just to the left of the sequencers in the 2nd picture.

    Relay wiring diagram:
    - Pins 1 & 3 coil
    - Pins 4-to-5 in default state
    - Pins 4-to-2 in the activated/triggered state

    Thanks for the info hvac1000! :)
  • Oct 3, 2008, 08:34 AM
    Scottyp

    My relay is:
    1~~3 Coil
    2... 5
    .\
    ... 4

    How would the 6 pin relay wire up?
    1~~3 same as old relay wiring
    5___6 same as old 5; 6 not used
    2___4 same as old 2 & 4

    Diagrams are different for triggering.. between my 5pin & 6 pin
  • Oct 3, 2008, 11:16 AM
    hvac1000
    Glad to help
  • Oct 3, 2008, 12:32 PM
    Scottyp

    Purchased the relay at Grangers today..
    Now, how do I make the connections?

    My old Relay is Normally Closed on pins 4 & 5
    The new 6 pin relay Normally Closed is pins 5 & 6 and Normally open on pins 2 & 4.

    http://i266.photobucket.com/albums/i...p/DSC04332.jpg


    How do I wire pins 2, 4 & 5 from the old relay?
  • Oct 3, 2008, 01:12 PM
    hvac1000
    Looks like 5 and 4 are normally closed according to your wiring diagram then 4 and 2 activate upon 24 volt power.

    Try putting a jumper between 4 and 5 also attaching the original wires to the respective terminals. Then attach the number 2 wire to the number 2 terminal.

    Here is what should happen. When the new relay is not activated tabs 4 and 5 will be together just like the old relay. When 24 volt power is applied terminals 2 and 4 will be activated droping terminal 5 out.
    You might test this using 24 volts to activate and unactivate the relay and your meter to make sure I am correct.

    NOTE no changes necessary for the 24 volt feed/activation wires. Just use the same numbers.
  • Oct 3, 2008, 01:36 PM
    Scottyp

    I have 5 wires..
    So should I wire as follows:
    #1 wire to #1 terminal
    #3 wire to #3 terminal
    #4 wire to #4 terminal
    #5 wire to #5 terminal
    #2 wire to #2 terminal
    Jumper between 4 & 5 terminals

    I would have thought to jumper terminals 4 & 6 to complete the circuit for normally closed...
  • Oct 3, 2008, 02:27 PM
    hvac1000
    You can jump between 4 and 5 or 4 and 6. They are actually the same terminal since they are jumped internally as long as the relay is not energized with 24 volts.

    I stated terminal 5 so as not to confuse the issue by adding another terminal number.
  • Oct 3, 2008, 04:36 PM
    Scottyp

    Cool..
    Installed the new relay.. just get a humm from the fan..

    Will investigate tomorrow.. and post results.
  • Oct 4, 2008, 04:02 AM
    hvac1000
    On thing you might do is to jump or remove the relay from the equation then see if the blower motor runs.
  • Oct 4, 2008, 07:33 AM
    Scottyp

    What wires do I jump? Coil wires?
  • Oct 4, 2008, 10:17 AM
    hvac1000
    NO do not jump the coil wires those are 24 volt and it will burn something out since that will cause a direct short in the low volt system.

    Disconnect wire on tab 5 or 6 depending upon which tab you used (see other discussion on this) then Jump 4 and 2 and see what happens. This way you are making direct contact for voltage to the motor and the motor should run.

    Put wires back where they were
    Then
    Then try disconnecting 2 and jumper 4 and 5 and see what happens


    NOTE: this is the W/R page for this relay..


    http://www.white-rodgers.com/wrdhom/..._06_pg0115.pdf
    I hope during this entire process you have identified all the wires that are being used on this relay. If they get mixed up you will have to trace back and that will take all the fun out of it.
  • Oct 4, 2008, 12:37 PM
    Scottyp

    Thanks for the info. Will test it later today.

    Wires are labeled by number...
  • Oct 6, 2008, 06:01 PM
    Scottyp

    Okay guys.. Im back home. Had to go out of town for a short trip..

    Here's the test results from Saturday:

    Installed the new relay and wired per instructions. All I get is a constant hum from the fan with thermostat is in off position.

    Jumpered relay wires 2 & 4 to test the fan. The fan comes on.

    So, I reinstalled old relay. It gives me the same results. Now, my fan only comes on with jumpered wires 2 & 4.

    What changed?
    Don't make any sense as I haven't changed anything else..
    What should I test next?
  • Oct 6, 2008, 06:15 PM
    hvac1000
    If 2 and 4 when jumpered works the fan then something is wrong with this picture.

    When the unit is in the A/C mode check for 24 volts on pin 1 and 3. There should be 24 volts there and the relay should pull in to activate the fan.

    If 24 volts is not present then another device is holding the 24 volts from getting to the relay.

    The only other possibility is that we have the relay wired backwards but I really do not think so.
  • Oct 6, 2008, 06:29 PM
    Scottyp
    Quote:

    Originally Posted by hvac1000 View Post
    If 2 and 4 when jumpered works the fan then something is wrong with this picture.

    When the unit is in the A/C mode check for 24 volts on pin 1 and 3. There should be 24 volts there and the relay should pull in to activate the fan.

    If 24 volts is not present then another device is holding the 24 volts from getting to the relay.

    The only other possibility is that we have the relay wired backwards but I really do not think so.

    Hey HVAC.. Thanks for the response..

    Agreed, something is wrong with this picture... First, I have always on fan. Now I have a always hum and instead of the fan on...

    But before I go up in the attic to check for 24v on pins 1 & 3, I just completed a little test that sort of did the same thing... I changed the fan setting on thermostat from auto to ON always. Turn on power at air handler and the fan came on..

    But I like your test better... I post again in 30 min..
  • Oct 6, 2008, 07:12 PM
    Scottyp

    Maybe I'm doing something wrong, but I don't get 24v on 1 & 3. I put the positive DVM on terminal 1 and negative DVM on ground = 0. Same on #3 terminal.

    Did I do this correctly?
  • Oct 6, 2008, 07:20 PM
    hvac1000
    Set the volt meter for the scale that will read the 24 volt circuit.

    Then disconnect both wires from the relay.
    Then attach the meter to the two wires and see if you have 24 volts when the system is in the A/C mode. If not try the fan on mode on the thermostat and test again. I never trust the frame ground for testing. Test using the wires only. They must be disconnected from the relay for the test.

    If you do not have 24 volts there you are going to have to trace back to find the 24 volts and the reason it is not getting to the relay.
  • Oct 6, 2008, 07:32 PM
    Scottyp

    Will do.. Back to the attic I will go..

    My DVM has Vac, Vdc, Aac, Adc, Ohm, F, & uFarads.
    Ive been using Vac.
  • Oct 6, 2008, 08:17 PM
    Scottyp

    Attached to the removed two wires; 1 & 3.
    In A/C mode = 0
    In Fan On = 26.2
  • Oct 6, 2008, 09:10 PM
    hvac1000
    The relay should be activated in the A/C mode.

    See below

    http://customer.honeywell.com/techli...0s/69-0392.pdf

    See section 5
    When C1 makes it triggers the fan relay through the on off fan switch in the off position.

    Now I am starting to believe there could be a problem with the wiring at the thermostat. Why it worked for a few days is anyone's guess.
  • Oct 7, 2008, 08:05 AM
    Scottyp

    Okay..
    Last night, I noticed that the new relay was melting at terminal #3. The plastic started to deform.

    So, I put back the original relay and tested the heat cycle (as it was cool last night here). Everything worked fine except for the hum when fan was off. The fan went off during the system off stages and the fan came on with the heat pump during the heating stage. Everything works as programmed.

    Changed the Thermostat to AC this morning and the old symptoms returned: Fan hum always and the Heat Pump/fan goes on & off as called by the thermostat. Then I set the Thermostat to OFF but the fan continues to hum.. This is strange.
    Killed the power and came to work.. :(

    Im now thinking that it is the Thermostat wiring too. The new relay wiring is also suspect but Im ordering a new original York relay just to be safe. Also still wondering about the high transformer reading.

    Thermostat wiring connections:

    Old = New
    R = R and Rc Jumpered
    Y = Y
    G = G
    O = O/B
    W = Aux
    B = C
    X = E

    .