  • Dec 4, 2007, 07:21 PM
    darque
    Heater fine daytime, stops at night!
    Heater is gas forced air and works fine in higher temperature daytime if in 60's, 70's. But if colder it won't turn on unless thermostat is manually moved back down then up so mercury trips again. Even had a hvac friend come out, test all of it, he replaced something but still same problem even after he checked it again but always during the day when it works fine. I put a new thermostat (non mercury switch) before he came and it didn't solve it either. It will go as hot as you want during the day and you can just put therm at 80 and it will go there. But when cold outside the only way to get it on for a few minutes each time is to rock the mercury and slowly creep up the setting, which I can't do from bed asleep. Any help appreciated:confused:
  • Dec 4, 2007, 08:28 PM
    wmproop
    I`m confused,, you do or don`t have a non-mercury thermostat,on it right now?
  • Dec 4, 2007, 09:17 PM
    labman
    There is a simple furnace/thermostat test at https://www.askmehelpdesk.com/heatin...ons-58313.html
  • Dec 7, 2007, 03:15 PM
    darque
    Quote:

    Originally Posted by wmproop
    i`m confused,,,you do or don`t have a non-mercury thermostat,on it right now?

    I have the original mercury Honeywell thermostat T8195B on it. I put on a non mercury one and heater still acted same way so I put original mercury therm back on.

    The mercury contact works and completes circuit and turns on heater but when it's below a certain temp it won't keep cycling.

    I just noticed now on a colder day that only the merc swtch for the blue lever is making the rheem criterion come on or off whether the therm is set to heat or cool. The other merc switch connected to red lever doesn't turn the rheem on or off when therm is set to heat or cool. Where can I find a manual for this thing? Thanks
  • Dec 7, 2007, 04:37 PM
    hvac1000
    Manual and install

    http://customer.honeywell.com/techli...0s/69-0563.pdf

    http://customer.honeywell.com/techli...0s/69-0564.pdf
  • Dec 11, 2007, 01:58 PM
    darque
    Quote:

    Originally Posted by labman
    there is a simple furnace/thermostat test at https://www.askmehelpdesk.com/heatin...ons-58313.html


    Therm for heat works fine if the outside temp is 65 or above but if it's 50 outside it just burns for a minute or less and blows for maybe 3 or 4 short cycles a minute or so a piece and then stops without the mercury moving at all. If I then just rock the mercury once it will start again and go through the same 3 or 4 short cycles for about five minutes total and stop again with the mercury still sitting in same spot... thoughts?:confused:
  • Dec 11, 2007, 04:47 PM
    hvac1000
    Jump the thermostat for the heat cycle. White (W) and Red (R) should do it. It might be easy to do this back at the furnace unless you want to take the stat apart. When it cold and it will not run jump it out and let it run. If it runs it is the tstat if it stops running like it has before it is a furnace problem.

    Simple test
  • Dec 12, 2007, 12:25 PM
    darque
    Quote:

    Originally Posted by hvac1000
    Jump the thermostat for the heat cycle. White (W) and Red (R) should do it. It might be easy to do this back at the furnace unless you want to take the stat apart. When it cold and it will not run jump it out and let it run. If it runs it is the tstat if it stops running like it has before it is a furnace problem.

    Simple test


    Thanks for the help, u mean to connect W and R correct?
  • Dec 12, 2007, 01:16 PM
    hvac1000
    Yes
  • Dec 14, 2007, 03:38 PM
    darque
    Quote:

    Originally Posted by hvac1000
    yes

    Aha, jumped r & w and same thing, just heats for a few minute long cycles then stops. And then disconnect r/w and reconnect it starts again with same behavior. Thoughts appreciated on what next... :confused:
  • Dec 14, 2007, 03:48 PM
    hvac1000
    The trheremostat seems to be OK.
    Make sure the air filter is clean or replace it.
    Does the blower fan ever come on?
    If not that could trip a oevrheat safety shutting the furnace off.
    Whenever you cycle the thermostat you are you are doing a reset of the control and that is why it comes back on.
  • Dec 14, 2007, 04:47 PM
    darque
    1 Attachment(s)
    Quote:

    Originally Posted by hvac1000
    The trheremostat seems to be OK.
    Make sure the air filter is clean or replace it.
    Does the blower fan ever come on?
    If not that could trip a oevrheat safety shutting the furnace off.
    Whenever you cycle the thermostat you are you are doing a reset of the control and that is why it comes back on.

    Blower does come on. Filter is clean but is there a way to test it's not the filters like taking out altogether for a test or.. because it has a funny set up as you see in the pic. The heater is off the ground about a foot high and directly under it is the filter. But also there is a filter in the door of the closet as well. I've taken the door filter out. (as you see it laying on floor in picture) left door hang open, etc. to try see any change but no luck, ideas? (btw the AC has no issues if it matters) thanks, I really want to solve this:(
  • Dec 14, 2007, 06:55 PM
    hvac1000
    There is something wrong with the install of your furnace according to the pictures. Your return air is supposed to be totally isloated from the combustion air for the burner. There is a grill there in the door but I see no effective way to seal it off. Since the furnace is in a closet it is supposd to be feed combustion air from the outside. Now I will admit those pipes might be somewhere there but they do not show on the picture. See if you can take a few more pictures.

    I am just wondering if this setup is causeing some or all of the problems.
    Your main complaint really does not make sense to me because the furnace should run no matter what the outside temp is to start with.

    BTW there is NO storage allowed in that closet also. Just thought I would mention that fact.
  • Dec 14, 2007, 07:46 PM
    wmproop
    Now! my friend you have determined that your problem is in the furnace not in the thermostat, have you checked and cleaned the flame senser,,
  • Dec 14, 2007, 08:55 PM
    kanrdc
    Quote:

    Originally Posted by darque
    heater is gas forced air and works fine in higher temperature daytime if in 60's, 70's. but if colder it won't turn on unless thermostat is manually moved back down then up so mercury trips again. even had a hvac friend come out, test all of it, he replaced something but still same problem even after he checked it again but always during the day when it works fine. i put a new thermostat (non mercury switch) before he came and it didn't solve it either. it will go as hot as u want during the day and u can just put therm at 80 and it will go there. but when cold outside the only way to get it on for a few minutes each time is to rock the mercury and slowly creep up the setting, which i can't do from bed asleep. any help appreciated:confused:

    Need more info to help you. Make, Model, 90% or conventional venting, standing pilot or electronic ignition? First guess is cooler air is condensating your electronic ignition down your flue pipe. Contact me with more info, I will be glad to help if I can.
  • Dec 14, 2007, 09:54 PM
    labman
    Note to kandrc: Site policy is not to ask or answer questions by PM or email.

    You are asking some good questions. Many of the better people on this forum are AWOL. We could use another good man.
  • Dec 14, 2007, 10:36 PM
    hvac1000
    Check all the 120 volt wiring especially the ground circuit from the house oanel to the furnace switch. Then check to make sure the bare or green ground wire lands in the furnace. Also check all ground wires in the furnace for tightness.

    Post your model and brand name so I can pull a diagram if I have one.
  • Dec 15, 2007, 07:44 AM
    wmproop
    Quote:

    Originally Posted by darque
    thnx for the help, u mean to connect W and R correct?




    \\\ok,, now you have determined,the thermostat is bypassed and you still have the prob. somust be in the furnace,, have you checked and cleaned the flame senser?
  • Dec 15, 2007, 02:26 PM
    darque
    3 Attachment(s)
    Quote:

    Originally Posted by hvac1000
    Check all the 120 volt wiring especially the ground circuit from the house oanel to the furnace switch. Then check to make sure the bare or green ground wire lands in the furnace. Also check all ground wires in the furnace for tightness.

    Post your model and brand name so I can pull a diagram if I have one.

    Thanks for everyone's help, we'll get this...

    Some more pictures. It seems as if it is some switch or sensor getting automatically tripped but it doesn't need anytime to dry or cool down or anything to restart it, just rock the mercury two seconds after it stops its four minute cycle and it goes again for the same four minutes. When it's running it all functions well so would that rule out a grounding issue?

    And the reason it runs fine when indoor/outdoor temp is warmer is as I've observed the mercury is moving back and forth with rise and fall of temp. it just needs to run longer when it's colder outside/inside:confused:
  • Dec 15, 2007, 02:27 PM
    darque
    Rheem criterion gas furnace
  • Dec 15, 2007, 03:37 PM
    hvac1000
    It is hard for me to see but if the thermostat has a adjustable heat anticipator try incerasing it. Usually there is a arrow that says longer with the direction to mover it.

    What is the model number and brand thermostat. I will see if I can look it up.
  • Dec 15, 2007, 04:43 PM
    labman
    Browse the sticky at https://www.askmehelpdesk.com/heatin...ons-58313.html

    Next time it won't start do the furnace/thermostat test. If it still won't start, post back with what point in the sequence it fails.
  • Dec 17, 2007, 01:36 PM
    darque
    Quote:

    Originally Posted by wmproop
    \\\ok,,,now you have determined,the thermostat is bypassed and you still have the prob.,somust be in the furnace,,,have you checked and cleaned the flame senser?


    How can I check and clean the flame sensor? It's a rheem criterion gas furnace, pictures of the setup on page 2 of this thread, thanks
  • Dec 17, 2007, 01:38 PM
    darque
    Quote:

    Originally Posted by hvac1000
    It is hard for me to see but if the thermostat has a adjustable heat anticipator try incerasing it. Usually there is a arrow that says longer with the direction to mover it.

    What is the model number and brand thermostat. I will see if I can look it up.


    Honeywell thermostat T8195B, thanks
  • Dec 17, 2007, 01:41 PM
    darque
    Quote:

    Originally Posted by labman
    Browse the sticky at https://www.askmehelpdesk.com/heatin...ons-58313.html

    Next time it won't start do the furnace/thermostat test. If it still won't start, post back with what point in the sequence it fails.


    Always the same behavior, just a total of a few minutes consisting of maybe 5 or 6 burn and blow cycles then no more and that is with jumping red and white with no thermostat... :(
  • Dec 20, 2007, 10:22 PM
    labman
    Ok, if you have the problem with the red and white connected, it is a furnace problem, not at thermostat problem. Go back to the sticky and note where in the start up sequence it fails.
  • Dec 21, 2007, 07:26 PM
    T-Top
    When you move your t-stat down than back up you are resetting the control board.Its called a soft start by breaking 24v on the W circuit. If it was a major problem you would need to kill the power going to the unit to get it to reset or manually press a button inside the furnace(hard start). If you are using LP you may have moister in your tank, in cooler temps the regulator will freeze and starve the system for gas. That system should have a diagnostic light to tell you why it locked out.
  • Dec 24, 2007, 01:20 PM
    darque
    Quote:

    Originally Posted by T-Top
    When you move your t-stat down than back up you are resetting the control board.Its called a soft start by breaking 24v on the W circuit. If it was a major problem you would need to kill the power going to the unit to get it to reset or manually press a button inside the furnace(hard start). If you are using LP you may have moister in your tank, in cooler temps the regulator will freeze and starve the system for gas. That system should have a diagnostic light to tell you why it locked out.


    Actually just gas line coming in so no tanks and still can't figure this thing out but thanks for any other ideas
  • Dec 24, 2007, 01:56 PM
    darque
    2 Attachment(s)
    MY POST TITLE IS INCORRECT, IT SHOULD BE - "HEATER ONLY WORK FOR FIVE MINUTES ANYTIME" temp does not make a difference

    Here's more pics with a question, is the sensor in yellow circle the flame sensor? Has markings on the bottom "TOD J1" has no corrosion on it but should I try a new one and if so where in los angeles can I get one?

    Other thing is the rod I thought was the flame sensor has no wires connected to it at all so what is this rod circled in red in the picture. It can slide left to right about and inch but can't come out without taking the whole assembly out, thanks guys for any help.

    And other info is that by jumping red and white it will do the five minutes as noted in my other posts but it doesn't matter what the temp is outside, cold or warm it will only do that five minutes with R/W jumped. There are 4 wires you see me holding that all run to a square coil or ? But as you see not connected to anything, make a difference for the heater?
  • Dec 24, 2007, 02:09 PM
    darque
    2 Attachment(s)
    There are 4 wires u see me holding that all run to a square coil or ? But as u see not connected to anything, make a difference for the heater?[/QUOTE]


    Actually a correction, those 4 wires (2 yellow, 1 WHT, 1 BLK) run to a small white plastic box, not a coil, box circled in green in photo
  • Dec 24, 2007, 03:07 PM
    hvac1000
    Yellow not actually a flame sensor. It is a rollout type overload that senses when the flame or too much heat is coming out of the furnace from the wrong place. That should not happen at that location for normal operation and it should not have to be pushed to reset unless there is a problem.

    Do the two burners light off and burn normally? Blue with a bit of yellow tips?
    Do you have to reset that switch in yellow?
  • Dec 26, 2007, 12:24 PM
    darque
    Quote:

    Originally Posted by hvac1000
    Yellow not actually a flame sensor. it is a rollout type overload that senses when the flame or to much heat is coming out of the furnace from the wrong place. That should not happen at that location for normal operation and it should not have to be pushed to reset unless there is a problem.

    Do the two burners light off and burn normally? Blue with a bit of yellow tips?
    Do you have to reset that switch in yellow?


    Flames burn blue real good. I noticed that they burn for 20 seconds then go off, then the fan goes on for 30 sec, then off and ignitor glows and another 20 sec off flame, then off, then fan on for 30, etc. this is the usual cycle that lasts about 5 minutes then nothing until I re jump red and white. One question is should the fan be coming on while the flame burns or is it proper for them to alternate?

    Any help on where the flame sensor is on this rheem criterion II and how to clean it? Thanks
  • Dec 26, 2007, 12:55 PM
    hvac1000
    Sounds like a flame sensor problem to me unless that pilot is a 3 wire set up then it could be bad.
    I have not followed this thread but have you cleaned the pilot orifice?
  • Dec 26, 2007, 02:07 PM
    darque
    Quote:

    Originally Posted by hvac1000
    Sounds like a flame sensor problem to me unless that pilot is a 3 wire set up then it could be bad.
    I have not followed this thread but have you cleaned the pilot orifice?


    Can u look at the picture and tell me if u see a flame sensor? Thanks
  • Dec 26, 2007, 05:34 PM
    hvac1000
    I do not see a flame sensor but I do see a HSI (hot surface ignition system).

    The blue line area item is a hot surface ignitor device. It should glow then the furnace should lite.

    Are you on LP gas/Propane if so there could be a 5 minute lock out on your furnace?

    See circuit board for a code flashing from a green LED. Open the blower door so you can see the PC board. Push the safety door switch and wait for the middle LED to start flashing a repeating code. On the blower door there is a flow chart of operation and a key to the code. THis may indicate a problem code.

    Integrated control board and for some reason the ignitor is "locking out" for some reason.
  • Dec 27, 2007, 11:42 AM
    Mogwai
    Hi Darque, and everyone else, I currently have just about the same problem, actually I think it is. I've done some research and want to clean my "flame sensor" but can't find one. Heating igniter glows for 10-15 seconds then shuts down, tries 2 more times then locks down, in which I either go to thermostat and turn off and back on OR turn power switch off and back on that is located on side of furnace. Here is the part that I think should help solve our dilemma. Once I get mine going(after reseting it a gazillion times, my furnace will run properly until I turn it down to go to bed, then in the morning I go play ball with it again. I also have a Rheem/Rudd furnace and it worked fine from Oct through November(michigan). And like I said, I believe the next step is cleaning the flame sensor which I can't find. I will provide pictures tomorrow.
  • Dec 27, 2007, 12:11 PM
    hvac1000
    The sensor in this unit is called a remote flame sensor. That is all I know.
  • Dec 27, 2007, 06:54 PM
    T-Top
    The hot surface ignitor is the flame sensor also with this style of unit.
  • Dec 27, 2007, 07:03 PM
    T-Top
    Don't try to clean it you will only break it. If its glowing that is not your problem.
  • Dec 28, 2007, 11:55 AM
    darque
    Quote:

    Originally Posted by T-Top
    Dont try to clean it you will only break it. If its glowing that is not your problem.

    Thanks t-top, it does glow fine. Could it be glowing fine but still have a problem with being too sensitive for monitoring the flame from age?