Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   No Power to A/C Thermostat (https://www.askmehelpdesk.com/showthread.php?t=354000)

  • May 16, 2009, 11:31 AM
    KenLoh
    Quote:

    Originally Posted by Joshdta View Post
    Ok where is the third red wire going? from the wire bug?

    The 3rd red wire goes into one of the 3 brown wires you see in the pic.

    1st brown wire goes into the ceiling, which I believe leads to the tstat.

    2nd brown wire only has a black and a red (the rest are cut off) that goes to the white pvc pipe going into the floor, which I described earlier. This could be a sensor, or something... I don't know.

    3rd brown wire also goes into the floor, this one I believe goes to the rear condenser.
  • May 16, 2009, 11:38 AM
    KenLoh

    I'm puzzled here, if there is 26V between R and W1, G, C
    And R is connected to the wirenutted 3 reds
    Why is there no power between the 3 reds and W1, G, C?

    http://img194.imageshack.us/img194/8...rfusevac03.jpg
  • May 16, 2009, 11:44 AM
    KenLoh
    [QUOTE=KenLoh;1739209]I'm puzzled here, if there is 26V between R and W1, G, C
    And R is connected to the wirenutted 3 reds
    Why is there no power between the 3 reds and W1, G, C?

    Never mind... my bad... black is not connected to the 3 reds, Let me double check.
  • May 16, 2009, 11:44 AM
    KISS

    Josh is on the right track. I'll not be available for much of today.

    At this point I see a serious thermostat wiring problem and you may just have to chase them down.

    You have:

    The air handler terminals and colors to two different cables. 1: ouside, 2 thermostat

    The thermostat has colors and terminals.

    There should be one loose end at the air handler.

    Terminal Y of the stat heads outside, so it jumps cables. In real system, this would be the yellow wire. So, it alone would have a wire nut.

    This looks like an electric furnace and not a heat pump.

    You should have a table like:

    Tstat
    1-Red to R
    1-Blue-to C

    Etc

    Outside unit (only two wires are connected)
    2-Red to ouside contactor
    2-yellow to outside contactor
    2- Brown (No connection(

    Air handler
    R to 2-Red
    R to 1- Red
    C to 2-blue

    1-brown (wrapped or not connected)

    The 1 refers to the cable to the stat
    The 2 refers to the cable to the AC unit

    If you can put this together Josh should be able to help you figure it out.
  • May 16, 2009, 12:01 PM
    KenLoh

    The wires on my tstat are
    Red-R
    Green-G
    Yellow-Y1
    White-W2
    Orange-W1/O/B
    Nothing-Y2
    Blue-C
  • May 16, 2009, 12:49 PM
    KISS

    In reality, you need a 3 stage heat, and probably 1 stage cool. The tstat is a 2 stage heat and 2 stage cool.

    It can be made to work with a couple of jumpers, but the right stat might be more energy efficient.

    Generally, you can have more stages than required, but you should not have less.

    I think you have an electric furnace with 3 stage heat and one stage cool. Am I correct?

    Jumping the terminals at the furnace should cause things to happen.

    I think in an electric furnace, I'm not sure what controls the fan, It's eitier the furnace or the thermostat.

    At the furnace:

    R jumped to G; turns on fan
    R jumped to W; turns on heat and may turn on fan sometime later.

    Check that as it stands.

    Also go outside and follow the thermostat wires and take a picture of that. There should be two wires and two power wires going to the same object.

    Make sure the new thermostat has an electric furnace option in it's setup.

    It looks like you had the wrong thermostat from the get go.

    I think that power is not getting to the stat because the R wire is out of place. It's also why the AC doesn't work.

    I'm getting ready to start over.
  • May 16, 2009, 12:53 PM
    KISS
    If the tsat has:
    1) an electric option
    2) R to G at the furnace turns on the fan
    ... R to W1 turns on the heat (note fan behavior, it may be delayed) Connect for no more than about 5 minutes

    Are you ready to rip all of the t-stat wires out and start over?
  • May 16, 2009, 12:57 PM
    KISS

    I hope you don't have a heat pump with emergency heat. If that were the case the outside unit would run in heating and cooling mode.

    Am I correct that the outside unit doesn't run when heating?
  • May 16, 2009, 01:04 PM
    KenLoh
    Quote:

    Originally Posted by KeepItSimpleStupid View Post
    I hope you don't have a heat pump with emergency heat. If that were the case the outside unit would run in heating and cooling mode.

    Am I correct that the outside unit doesn't run when heating?

    I can't recall... I think the outside unit runs when heat is on. I thought it did, until you ask, I'm not sure.
  • May 16, 2009, 01:07 PM
    KenLoh

    I have tried jumping wires at the tsat, nothing happens. R to G, R to Y... even waited a few minutes... nothing, not even fan.

    I have also connected the R(black) to Green at the air handler... nothing, no fan.
    Or should it be Green to C instead?
  • May 16, 2009, 01:07 PM
    KISS

    OK, time to take a picture of the outside unit where the tstat wires go.
  • May 16, 2009, 01:20 PM
    KenLoh
    Quote:

    Originally Posted by KeepItSimpleStupid View Post
    In reality, you need a 3 stage heat, and probably 1 stage cool. The tstat is a 2 stage heat and 2 stage cool.

    It can be made to work with a couple of jumpers, but the right stat might be more energy efficient.

    There is no power at the wires coming out of the wall to the tstat.

    Quote:

    Generally, you can have more stages than required, but you should not have less.

    I think you have an electric furnace with 3 stage heat and one stage cool. Am I correct?
    I don't understand what a 3 stage heat or 1 stage cool mean, sorry.

    Quote:

    Jumping the terminals at the furnace should cause things to happen.

    I think in an electric furnace, I'm not sure what controls the fan, It's eitier the furnace or the thermostat.

    At the furnace:

    R jumped to G; turns on fan
    R jumped to W; turns on heat and may turn on fan sometime later.

    Check that as it stands.
    I've tried R to G - nothing happened. I'll try again. Will the fan work with the air handler panel open? I did jump then close the panel just to be sure. Nothing happened either.

    Quote:

    Also go outside and follow the thermostat wires and take a picture of that. There should be two wires and two power wires going to the same object.
    The tstat wires that go to the rear condenser unit, runs underground, I think. If you look at the first few pics I posted of the condenser, you should be able to see them in there.

    Quote:

    Make sure the new thermostat has an electric furnace option in it's setup.

    It looks like you had the wrong thermostat from the get go.

    I think that power is not getting to the stat because the R wire is out of place. It's also why the AC doesn't work.

    But everything was working fine for 6-1/2 yrs.
  • May 16, 2009, 01:23 PM
    KISS

    IT looks like you have a Heat Pump and you did take a pic of th ouside unit. I just missed it. There are a BUNCH of wires connected to a terminal strip.

    What are the designations and colors.

    I hope you bought a heat pump thermostat with the right amount of stages.
  • May 16, 2009, 01:23 PM
    KenLoh
    Quote:

    Originally Posted by KeepItSimpleStupid View Post
    OK, time to take a picture of the outside unit where the tstat wires go.

    The first pic that I posted in this thread, does that help? IF not I'll go take a closeup.
    I tested there, no power at those 24V terminals.
  • May 16, 2009, 01:27 PM
    KenLoh

    I kind of got diverted to focus on the air handler side, and ruled out the outside condenser. Could that circuit board where the 24V terminals are on, be faulty?
  • May 16, 2009, 01:29 PM
    KenLoh
    Quote:

    Originally Posted by KeepItSimpleStupid View Post
    IT looks like you have a Heat Pump and you did take a pic of th ouside unit. I just missed it. There are a BUNCH of wires connected to a terminal strip.

    what are the designations and colors.

    I hope you bought a heat pump thermostat with the right amount of stages.

    KISS... I think you misunderstood. I did not buy a new tsat. Was going to, but since there is no power from the wires off the wall, I ruled out a faulty tsat.

    Should I get a new tstat?
  • May 16, 2009, 01:36 PM
    KenLoh
    Quote:

    Originally Posted by KeepItSimpleStupid View Post
    There are a BUNCH of wires connected to a terminal strip.

    what are the designations and colors.

    Do you mean this terminal strip? Can you see from this larger pic?

    http://img36.imageshack.us/img36/3148/condenser04.jpg
  • May 16, 2009, 02:09 PM
    Joshdta

    I think you are going to find that wherever the black wire and the 3rd red wire goes is going to be your problem. A temp sensor, or a pressure swith maybe
  • May 16, 2009, 02:12 PM
    KenLoh
    Quote:

    Originally Posted by Joshdta View Post
    I think you are going to find that where evre the black wire and the 3rd red wire goes is going to be your problem. a temp sensor, or a pressure swith maybe

    Josh, I just found out that black and red (split from 3 red wirenut) that leads to the pvc pipe is a switch/sensor for overflow.

    Hold on, I just took some pics of the air handler and pipes etc. Should give a better idea of what kind of heater/system I have.
  • May 16, 2009, 02:16 PM
    Joshdta

    For like drain water? This could defentally be your problem

  • All times are GMT -7. The time now is 12:33 AM.