-   -   Rheem gas furnace RGDE 07NMAGR, fan comes on but nothing else (https://www.askmehelpdesk.com/showthread.php?t=819324)

  • Dec 13, 2015, 01:08 PM
    parttime
    Yeah, that shouldn't keep the ignitor from getting hot, only shut it off quick.
  • Dec 15, 2015, 12:57 AM
    Riles530
    I'm stumped, had to call a specialist, I'm betting on the (hot surface igniter module) being the issue, I'll find out in the morning, I'll pass it along, thanks for the assistance, with your help, I have a little better understanding of the proper operation of this unit
  • Dec 15, 2015, 04:39 AM
    parttime
    Thanks Riles, update will surely help someone else down the line.
  • Dec 15, 2015, 08:32 PM
    Riles530
    the hose from the induction blower to pressure switch had a split in it at the end that I had shortened and re applied after testing the pressure switch and there was a loose/broken power wire on the side of the NEMA box that contains the module and circuit boards, thanks again for your assistance
  • Dec 16, 2015, 09:16 AM
    parttime
    Thanks for the update, I'm glad you're warm again.