Are you at all interested in fixing this the BEST way?
I'd like to try to scrap the TAY103A and use a better, although more complicated thermostat to set up, but you have to run two wires to an outdoor sensor someplace. My favorite spot is under a telco NID. Shady and free air. Is that difficult for your to do? Or want to do?
Take a look here which backs me up: Is fossil fuel kit needed with Honeywell VP IAQ stat? - Heating & Air Conditioning Forum - GardenWeb
The 8320 or the 8321 (dehumidification) would work nicely. honeywell dual fuel - iaqsource.com
See the install guides.
I liked the pics. You could have moved the wires out of the way so one could see the terminals.
With this setup, you can choose if you want to use a HP and when the gas furnace is used. By using emergency heat, you can force the system to use gas.
You'll need an outdoor sensor.
Meanwhile back to the current problem.
Can you go outside and take some pictures. Remember to disconenct the outside unit. There should be a schematic there on the removed door or somewhere. There should also be a circuit board domewhere. Take a pic of this. Also find the model # on the outside unit and look for any documentation that should have been left with the homeowner.
OK, so far.
What I'm really worried about in your current setup, is what the temperature is when the heat pump is turned off.
I found the TAYPLUS wiring diagram here: http://hvac.amickracing.com/Heat%20P...Tayplus103.pdf
X2 is really E; a TRANE exclusive and B is really C (Common).
"T" is probably used to measure outside temperature and can be discarded. It looks as if the ODT locks out the gas furnace at it's setpoint. If you wanted to operate the system better you would need a stat that utilizes the "T" terminal. That would be a thermister that would measure outdoor temperature and lock out the heat pump.
If I'm reading this correctly, it does appear that a dual fuel stat would be a better option. Since this is living space, dehumidification would be a good option.
So, you have a wiring diagram: 2H/1C with emg/aux heat. Heat pump. The heat pump will act stupid at low outside temperatures.
Make sense? B is not the complement of O in a trane system. X2 is E. Fun, isn't it?
I'm still suggesting the 8321 VP stat with an outdoor sensor. eBay sometimes is a good source for the stat.