Outside Air Conditioner Unit: Fan Spinning in Reverse
Recently I replaced the contact relay and the capacitor (dual capacitor) on my 2.5 ton Payne outside unit. I thought that I wired everything on to the new capacitor correctly by following the wiring on the old capacitor. However, when turning on the unit, the fan on the outside unit spun counterclockwise. The unit was Sucking In Air rather than blowing it out, which is bad for the unit.
Solution: Originally on my unit the Brown Fan wire went to the Fan position on the old capacitor. The other Light Colored Yellow Fan wire went to the Common position on the old capacitor. However, wiring it the same way on the new capacitor reversed the rotation of the fan, thereby causing the unit to Suck In Air. By reversing the Fan Wires on the new capacitor, the fan spun clockwise and the air was blowing out of the unit. On the new capacitor the Light Colored Yellow Fan wire was this time connected to the Fan position of the new capacitor and the Brown Fan wire was connected to the Common position of the new capacitor.
Note: If your compressor has a delay in starting, you may want to consider adding a hard start capacitor. This has two Black wires that are wired to the Compressor position of the capacitor and the Common position of the capacitor. Wiring order does not matter.
Crabman