No probem, if it has a jumper wire. Anouther thing you can do while you have the t-stat off the wall is to jump from r to y and see if it runs this will tell you if it is still a t-stat problem or if it is some where else.
![]() |
No probem, if it has a jumper wire. Anouther thing you can do while you have the t-stat off the wall is to jump from r to y and see if it runs this will tell you if it is still a t-stat problem or if it is some where else.
Ok, I did go to see if it had the jumper, it did not, so I placed a jumper in, still nothing out at the unit. I can push the contactor in and the fan outside will kick on. I forgot to check about the R-Y and seeing if the unit would run, what other T-stat checks can be done. There is resistance at the capacitor and voltage at the contactor.
As stated in above posts, your problem is not at the outdoor unit. Forget about the outdoor unit for now. The problem occurred when new stat was installed. Double check to make sure there is a jumper between rh, and rc. Then if this doesn't work, do the rh to why jump and see if indoor blower comes on. This is most important at this point. Don't worry about the outdoor unit for now. Do your test and see if indoor blower comes on, if it doesn't come on, then neither will the outdoor unit. IF jumping rh to why at stat doesn't work, then go to the inside unit and jump are to why at the control board on furnace, let us know what you find and we will help you get this thing licked. Good luck and hope to hear from you soon.
Why do so many D.I.Y. thermostat replacements go wrong? :confused:
Ok sounds good, I will check, the problem I have it that the furnace worked for 4 months since I changed the T-Stat. However once I put the jumper wire in, the furnace didn't kick on either?
Does anything work on the furnace now? May have blown a 3amp fuse. Its just hard sometimes for us to help fix a problem when we can't see the things you are doing. Just do one thing at a time and let us know. Start by jumping r to y at furnace control board. Also let us know if blower on furnace kicks on when thermostat is set to fan on.
Did you turn the power off while installing the jumper??
I did NOT turn the power off as it was simply adding a jumper, did I possibly fry the circuit board or something to that T-Stat? Because the Furnace had worked before.
Check the contol board for a small 3 amp car type fuse
OK, where might that control board be located? On or near the furnace?
Bottom door of the furnace.
OK, Replaced T-Stat, looked for the fuse on the Circuit board and could not find one? The unit is a Trane TUE060A936K3.
HELP!
Nothing kicks on, you can hear the T-Stat Click to activate either one and nothing.
Before installing the jumper wire the Furnace worked, after nothing works (did not shut power off when installing jumper wire, of course there were sparks) all circuits in main circuit breaker are on and good.
If the power supply to the furnace has been on for some time, the transformer should feel warm to the touch. Turn power off before checking. If it's cool, uh-oh... something is wired wrong or shorted and burned the transformer.
Ok, and this transformer you speak of is there on the circuit board? I take it this particular circuit board does not consist of the "automotive" style fuse that can easily be replaced, it will most likely need a new Control Board, right?
OK, with this manual you have provided, what am I looking for in these? I mean it has schematics and such, but really isn't leading me into the whole solution realm.
If you're not getting it yet, it may be time to call in a pro.
Yes it could be, however I have only done what has been suggested. I installed the JUmper wire, when I did that I failed to shut the power off, so I might have either fried the Control board since I can't seem to locate a "quick" change fuse, I am supposing I will need to change the whole control board?
Well, maybe now you are getting it. "Supposing" as opposed to effective troubleshooting usually results in unnecessary parts changing to solve a problem. It's not likely that you "fried a board", but on-site diagnostics will almost always be more effective than internet help. Did you try my earlier suggestion (checking the transformer for warmth)?