  • May 2, 2009, 07:17 AM
    Joshdta

    No probem, if it has a jumper wire. Anouther thing you can do while you have the t-stat off the wall is to jump from r to y and see if it runs this will tell you if it is still a t-stat problem or if it is some where else.
  • May 9, 2009, 11:47 AM
    ballbrat1622

    Ok, I did go to see if it had the jumper, it did not, so I placed a jumper in, still nothing out at the unit. I can push the contactor in and the fan outside will kick on. I forgot to check about the R-Y and seeing if the unit would run, what other T-stat checks can be done. There is resistance at the capacitor and voltage at the contactor.
  • May 9, 2009, 12:09 PM
    oatmail
    Quote:

    Originally Posted by Joshdta View Post
    ok then is sounds like it is a t-stat problem then. if neither the indoor or out work.

    I totally agree here. I just want to add that the jumper he is talking about is from Rh to Rc, a typo I'm sure. This is very common with stat replacements.
  • May 9, 2009, 12:48 PM
    mygirlsdad77

    As stated in above posts, your problem is not at the outdoor unit. Forget about the outdoor unit for now. The problem occurred when new stat was installed. Double check to make sure there is a jumper between rh, and rc. Then if this doesn't work, do the rh to why jump and see if indoor blower comes on. This is most important at this point. Don't worry about the outdoor unit for now. Do your test and see if indoor blower comes on, if it doesn't come on, then neither will the outdoor unit. IF jumping rh to why at stat doesn't work, then go to the inside unit and jump are to why at the control board on furnace, let us know what you find and we will help you get this thing licked. Good luck and hope to hear from you soon.
  • May 9, 2009, 01:46 PM
    KC13
    Why do so many D.I.Y. thermostat replacements go wrong? :confused:
  • May 11, 2009, 11:08 AM
    ballbrat1622
    Ok sounds good, I will check, the problem I have it that the furnace worked for 4 months since I changed the T-Stat. However once I put the jumper wire in, the furnace didn't kick on either?
  • May 11, 2009, 03:24 PM
    mygirlsdad77

    Does anything work on the furnace now? May have blown a 3amp fuse. Its just hard sometimes for us to help fix a problem when we can't see the things you are doing. Just do one thing at a time and let us know. Start by jumping r to y at furnace control board. Also let us know if blower on furnace kicks on when thermostat is set to fan on.
  • May 11, 2009, 03:55 PM
    Joshdta

    Did you turn the power off while installing the jumper??
  • May 14, 2009, 10:57 AM
    ballbrat1622
    I did NOT turn the power off as it was simply adding a jumper, did I possibly fry the circuit board or something to that T-Stat? Because the Furnace had worked before.
  • May 14, 2009, 04:50 PM
    Joshdta

    Check the contol board for a small 3 amp car type fuse
  • May 17, 2009, 05:35 PM
    ballbrat1622
    OK, where might that control board be located? On or near the furnace?
  • May 17, 2009, 07:22 PM
    Joshdta

    Bottom door of the furnace.
  • May 20, 2009, 07:28 PM
    ballbrat1622
    1 Attachment(s)
    OK, Replaced T-Stat, looked for the fuse on the Circuit board and could not find one? The unit is a Trane TUE060A936K3.

    HELP!

    Nothing kicks on, you can hear the T-Stat Click to activate either one and nothing.

    Before installing the jumper wire the Furnace worked, after nothing works (did not shut power off when installing jumper wire, of course there were sparks) all circuits in main circuit breaker are on and good.
  • May 23, 2009, 07:18 AM
    KC13
    If the power supply to the furnace has been on for some time, the transformer should feel warm to the touch. Turn power off before checking. If it's cool, uh-oh... something is wired wrong or shorted and burned the transformer.
  • May 23, 2009, 10:40 AM
    ballbrat1622
    Ok, and this transformer you speak of is there on the circuit board? I take it this particular circuit board does not consist of the "automotive" style fuse that can easily be replaced, it will most likely need a new Control Board, right?
  • May 23, 2009, 11:55 AM
    okotoks_metis

    Manual:
    http://www.trane.com/webcache/un/spl...n_01011999.pdf
  • May 23, 2009, 01:52 PM
    ballbrat1622
    OK, with this manual you have provided, what am I looking for in these? I mean it has schematics and such, but really isn't leading me into the whole solution realm.
  • May 24, 2009, 07:10 AM
    KC13
    If you're not getting it yet, it may be time to call in a pro.
  • May 24, 2009, 08:39 AM
    ballbrat1622

    Yes it could be, however I have only done what has been suggested. I installed the JUmper wire, when I did that I failed to shut the power off, so I might have either fried the Control board since I can't seem to locate a "quick" change fuse, I am supposing I will need to change the whole control board?
  • May 24, 2009, 09:41 PM
    KC13
    Well, maybe now you are getting it. "Supposing" as opposed to effective troubleshooting usually results in unnecessary parts changing to solve a problem. It's not likely that you "fried a board", but on-site diagnostics will almost always be more effective than internet help. Did you try my earlier suggestion (checking the transformer for warmth)?