Look at the burner area, there should be some small round switches with two wires going to each switch. There should be a little round button between the wires, push on this button and see if you feel a little click(like it engaged). These switches will be your flame rollout switches. As far as you limit, it should be located on the wall of the combustion chamber, it will also have two wires going to it. You will either have to test for voltage across this, or do a continuity test on the switch. To test for voltage, there should be 0 volts across swith terminals when there is a call for heat, if there is 24 volts, the limit is bad.