  • Jan 30, 2009, 07:45 PM
    IdahoBiker
    Quote:

    Originally Posted by KC13 View Post
    Say...is there a wire connected to "GH" on the circuit board?

    Just wanted to let you Guys KNOW that I Located a "Service Manual" (PDF Format) for the 397H Furnaces... So, "IF" anyone NEEDS it (all 16 Pages), I would be happy to Provide...
    I Finally Found a OEM Pilot Burner & Igniter (BOTH for $32.00 +FREE SHIPPING), putting it in right Now as a matter of Fact:confused: Wish I had found This Manual BEFORE I started this:eek:, probably took off More than I needed too... Oh well Guess I'll do some Cleaning.

    So What did You Guys say that I should Look for In the Wiring? :confused:
    I found some of the Problem (the Electrode was too far away from the Burner):( It was way past 1/4", more like 3/8" and Bent towards the Center)
    I removed the Flame Sensor, and Cleaned (But it wasn't too Bad)
    Will I NEED to Re-Adjust the Pilot Flame?
    Because of What I started this Post with, will I Need to Adjust the "Blower Off-Time Control"?