-   -   Carrier furnace doesn't ignite, but blower fan always on. (https://www.askmehelpdesk.com/showthread.php?t=296798)

  • Nov 15, 2009, 09:47 AM
    KC13
    Have you determined if the transformer has failed again? If so, list the screw terminals on the circuit board with thermostat wires connected - is "C" used? Does the system have a humidifier? We can probably ignore any possibility of any shorted line-voltage wires since the blower does run. Also, check the mounting of the circuit board. Dismount it and look for evidence of arcing against the enclosure. Assure that top edge of board is properly engaged in tabs on enclosure - they should alternate/stagger.
  • Nov 16, 2009, 07:41 AM
    spinn

    Yes, the transformer did fail again based on testing the line/load terminals.

    Screw terminal C is used for one of the thermostat wires. Why do you suspect terminal C has something to do with things?

    The system does not have a humidifier.

    I'll check the board.
  • Nov 16, 2009, 05:44 PM
    KC13
    If the "C" terminal/wire was unused, it could not cause the transformer to overload. Even if the wire or thermostat was shorted, it could only cause the heat to operate continuously. Thus, that door remains open...
  • Nov 16, 2009, 06:10 PM
    letmetellu

    KC13 in doing a great job in trying to help you get to the bottom of your problem. But I would like to ask one question. Since the transformer is bad which side is bad the high voltage wiring or the low voltage wiring.
  • Nov 24, 2009, 04:12 PM
    spinn
    Don't get me wrong letmetellu... I'm appreciative of KC13's responses. I was just asking the question to expand my knowledge, not to question the legitimacy of the response.

    The line side (Low Voltage) went bad.

    The parts guy told me to install a 3A blade fuse in between the load and the transformer, to protect the transformer from burning out again. Works fine now.
  • Nov 24, 2009, 04:21 PM
    KC13
    Quote:

    Originally Posted by spinn View Post
    Don't get me wrong letmetellu...I'm appreciative of KC13's responses. I was just asking the question to expand my knowledge, not to question the legitimacy of the response..

    I got that...
    Quote:

    Originally Posted by spinn View Post
    The line side (Low Voltage) went bad..

    Line (primary) side is line voltage, load (secondary) is low voltage.
    Quote:

    Originally Posted by spinn View Post
    The parts guy told me to install a 3A blade fuse in between the load and the transformer, to protect the transformer from burning out again. Works fine now.

    That restores your control power, but what caused the old transformer to overload and/or fail? Fuses are cheaper than transformers, so that's still progress.