  • Dec 21, 2008, 10:42 AM
    KC13

    Sorry, I remember now that you replaced this. So many threads, so little memory... you were getting 28v at gas valve during ignition trials but no click from valve? Is valve switch on?
  • Dec 21, 2008, 10:45 AM
    KC13

    What are the terminal designations on the gas valve - "TH" & "TR", or "P", "C", & "M"? If the latter is true, is there a jumper between "P" & "M"?
  • Dec 21, 2008, 11:22 AM
    razorface

    It is M and C and there is no jumper between m and p as p is blank
  • Dec 21, 2008, 11:30 AM
    KC13

    Okay, try this: set voltmeter to AC amps function (make sure probes are connected to the right inputs), attach one probe to "M" terminal and one to wire removed from "M" terminal. Now turn heat on and see if you measure any amperage during ignition trial (when you hear click from gas valve relay on circuit board). If you do but hear no click from gas valve, the valve is bad, likely stuck closed.
  • Dec 21, 2008, 11:31 AM
    razorface

    No click at the gas valve the switch is on
  • Dec 21, 2008, 01:17 PM
    KC13

    Did you measure any amperage?
  • Dec 21, 2008, 06:07 PM
    razorface

    KC13 and wmproop you guys did a lot to help me out and I greatly appreciate it. My problem was the als and now it is working and my house is now warm. Thank you!
  • Dec 24, 2008, 11:13 PM
    wmproop

    Continuity test,, the wireing on each end . Pull the wires loose from each limit switch and use the same tester to see if they are open
  • Dec 24, 2008, 11:17 PM
    wmproop

    razorface agrees: this post is better than the gospel

    Sorry to disagree,, nothing is better than the gospel