Gas valve on,fan switch auto and blower door must be on.
![]() |
Gas valve on,fan switch auto and blower door must be on.
You can leave the top door off,just to see if it's going to light. Do you hear water slushing in the inducer?
No water. But when I remove small grey tube from gas regulator, plug with my finger, the light turns solid red for about 6 seconds, then goes back to flashing twice.
Is there a way to tell if propane is getting to the furnace, its on at the pig, but...
Does the ignitor ever glow?
No glow
Ok,locate the pressure switch,do you see the rubber tube that is connected to the pressure switch?
2 actually. Small & grey. One in front of the other. One goes to inducer motor & the other splits and goes to the box where u can see the flame and the gas valve
OK,the tube that goes to the inducer motor hooks to the pressure switch on the other end.
Yes
Shut furnace off,remove tube from inducer only,power furnace and suck on the tube like a straw,you will hear a click keep sucking keeping a vacum on the tube until you see an ignitor glow.
Your furnace should have a plastic exaust pipe,does it vent through the roof or the side of the house?
Did that, it glowed, then when I stopped, it stopped glowing
Roof
Ok, two pipes?
Two pipes go up through roof
How cold is it outside?
19 degrees. And we just got DUMPED on with snow over the past 3 days
Most likely something is blocking the intake or exaust. It could be a chunk of ice or even a bird or wasp nest. When either pipe is restricted the pressure switch will not close.
K, check and make sure snow or ice is not covering the intake and exaust on the roof, I'm willing to bet you have a ball of ice over the intake.
You're a genius. Thank u so much! I will get someone up there tomorrow to try and clean out. Thank u again