I had the error light (3 blinks) on my Goodman gmt090-3b furnace. The vent van would start up but the gas would not turn on and the furnace would not fire up. I was able to fix it by cleaning out the little nipple that the vacuum hose runs into on the vent fan from the pressure switch (2" round thing with 2 yellow wires and the vacuum hose running out of it). I figured out it was clogged by taking the vacuum hose off the pressure switch and blowing into it (with the other end still attached to the vent fan). I couldn't get any air through it. So I removed the other end of the hose (now the hose is completely off) and stuck a little screwdriver down the hole and cleaned out the little hole. I put the hose back on (at the vent fan end) and was able to blow through it. I hooked the other end back to the pressure switch and it fired right up. It now works great. Thanks for the info above-- it really helped and saved me a lot of $.