  • Nov 2, 2011, 03:23 PM
    augblue
    In response to ljosr : I assume that you have a T-Switch with a 3 prong plug on the front. Mine has a 4 prong plug (red, black, white, green) So, you say if I remove the green wire from my T-Switch front plug, I should be all set? And I will not have an issue with proper grounding? Just what to clarify before I attempt this.

    Thanks.
  • Nov 5, 2011, 06:31 AM
    augblue
    This is PKA. This morning I took ljosr's suggestion and removed the GREEN connection from the Front Plug of my 6 Circuit Reliance Controls Pro/Tran Indoor Transfer Switch 20216A. No luck, the furnace is still not working off the Transfer Switch. (I do have power going to it and hear a hum)The other 5 circuits are working fine. It still seems to be some grounding issue (I guess?? ), but I am stuck. Any other suggestion would be greatly appreciated. Thanks.
  • Nov 5, 2011, 06:34 AM
    PKA
    This morning I took ljosr's suggestion and removed the GREEN connection from the Front Plug of my 6 Circuit Reliance Controls Pro/Tran Indoor Transfer Switch 20216A. No luck, the furnace is still not working off the Transfer Switch. (I do have power going to it and hear a hum)The other 5 circuits are working fine. It still seems to be some grounding issue (I guess?? ), but I am stuck. Any other suggestion would be greatly appreciated. Thanks.
  • Nov 26, 2011, 01:49 PM
    Artman60
    I just bought a Honda EU2000i generator and am having a similar problem. The generator is an inverter type generator which was supposed to eliminate these issues. My 25 year old ( came with townhouse) hot air furnace, and 1 year old gas water heater ( power vent, no chimney) won't play nice with my generator. One of my coworkers had this issue and bought a 1200 watt power conditioner ( Tripp Lite lc1200/Amazon $102) and it cured his problem, Mine is due in on Monday, will post if it cures my problem. I set my furnace up on a cord, so it will plug into power conditioner, which will plug into generator during power failures
  • Nov 28, 2011, 06:28 PM
    Artman60
    Good news and bad news, Bad news is I got to tell the wife another hundred bucks is gone, power conditioner did not work, good news is I ran into the engineering teacher at the school I was working at today, and asked him his opinion. He replied that he thought the people who suggested bonding the neutral and ground of the generator together were correct, and if I was worried about harming the generator, I could put an inline fuse between the two, offering them protection from each other. I did this and my generator ran fine, and the furnace and water heater also ran fine, so I should be in business next power failure. Artie
  • Oct 31, 2012, 07:48 AM
    Brianwat
    Here's the problem: Generators provide a ground that is a different than the House/utility ground. My coleman furnace has a logic board that recognizes that the ground is not the same and won't start up fro that reason. I wish I didn't buy this furnace.
  • Nov 6, 2012, 09:08 AM
    davechina
    I have the same issue: Furnace clicks on - then off. On... then off.. over and over. Sometimes it goes a bit further to the ignite phase but shuts down there, or a little farther at powering up the main fan.

    I noticed that with only the furnace connected to power (nothing else running of the generator) it never gets past click on-click off. But if I connect everything I can think of - freezers, lights, fans, neighbors refrigerators connected to external outlets, the furnace boots up normally.

    Not knowing anything about electronics I guessed that the when only connecting the furnace, the furnace circuitry senses the full brunt of any fluctuations/surges and stops. When everything else is connected too, the fluctuations/surges are distributed evenly across all the appliances and the furnace isn't so annoyed. Just an uneducated guess.

    I have a Briggs & Stratton 7000W with a Reliant 6 circuit switch.

    I asked the electrician who installed the transfer switch about this anomaly and he had no clue - suggested running everything to avoid the problem, but I'm not comfortable with that.
  • Nov 7, 2012, 01:48 PM
    luqui80
    I'm looking into connecting my Coleman Echelon furnace to a generator as well. So if the generator is connected to the house's electrical panel, wouldn't the ground then become the house's ground and not the generator's ground? I'm looking into getting one of the Interlock Kit's (interlockkit.com) and hoping this would solve the grounding problem.