Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   2008 4 ton Goodman heat pump doesn't switch into electric strip heat? (https://www.askmehelpdesk.com/showthread.php?t=434616)

  • Jan 12, 2010, 03:44 PM
    HVACmike
    2008 4 ton Goodman heat pump doesn't switch into electric strip heat?
    OK even when its 17*F out I can still here it running at night. So is this a problem? I mean it runs non stop.
  • Jan 12, 2010, 03:45 PM
    hvac1000
    Who set the unit up for proper operation?
  • Jan 12, 2010, 03:49 PM
    HVACmike

    A service technician installed the unit new t-stat wires and a new electrical box. The t-stat is not original itz from 2006.
  • Jan 12, 2010, 05:21 PM
    hvac1000
    The question you are asking can be answered in many different way since the outside unit can be controlled by the thermostat or a cut off thermostat out in the unit itself. When was this new work done? I am trying to get an idea if this is a new problem since the new thermostat or a existing problem?
  • Jan 12, 2010, 06:48 PM
    HVACmike

    The old unit was a split system Comfortmaker 12 seer heat pump with 5 kw heat strips,the new Goodman was installed: September 5 2008 and he installed 10 kw heat strips goodman p/n HKR-10. So its like in the 20's now and I can hear the compressor running. Even when in defrost the strips don't kick on. And when the unit turns off, the blower continues to run for at least 2 minutes. The Comfortmaker was installed BEFORE we bought the hose in 2006. Same yr the tstat was replaced.
  • Jan 12, 2010, 08:59 PM
    KISS

    See this:

    Post model numbers.

    The installer messed up.

    At 17F, the HP should likely be on AUX heat alone.

    You should have based on certain outdoor temp ranges. Not going into details.

    1. >x HP
    2. <x and >y HP+AUX heat
    3. Aux heat <z

    2. Is the temperature that the HP creates the same output as the heat loss of your house (balance pt). It's different for every house.

    3. determined by mfr

    Alternative methods in the thermostat can be used for 2.
  • Jan 13, 2010, 07:41 AM
    HVACmike

    I will get the model and serial#'s asap! I don't know what he did.
  • Jan 13, 2010, 07:44 AM
    HVACmike
    Model # GPH1348H21AC serial# 0809494294 R-22 refrigerant copeland scroll compressor. And the thermostat is a Honeywell programmable RTH5000 series the heater is usually set to 70 but some cases 72 or 68.
  • Jan 13, 2010, 08:12 AM
    HVACmike

    Here is a link to the YouTube video, here it shows what the unit looks like.

    YouTube - My goodman heat pump running agin......wmv
  • Jan 13, 2010, 08:20 AM
    KISS

    Here are two manuals:

    Install
    http://www.acdirect.com/xcart/images...cts/IO-313.pdf

    Parts list
    http://www.acwholesalers.com/EasyEdi...s%20manual.pdf
  • Jan 13, 2010, 08:29 AM
    KISS
    See the install manual page 7, items #6 and #7

    Electric heat should come on in defrost (2-3 min max).

    The outdoor thermostat is optional.

    The latter can be performed by some of the Honeywell Vision Pro thermostats, but you have to run a sensor cable from the stat to outside.
  • Jan 13, 2010, 08:33 AM
    HVACmike

    Thanks KeepItSimpleStupid did the video help any? I will look at the manuals asap!
  • Jan 13, 2010, 08:42 AM
    KISS

    I'm tethered to my cell. Video's are a bit pokey. I didn't look at it.
  • Jan 13, 2010, 08:52 AM
    KISS

    Not much info on the heat strips. Goodman HKR-15C Installation Instructions and Product Brochures

    Wiring Diagram comes with supplimental heat unit and is supposed to be posted on the unit.

    You may have two issues:

    1. Problem with defrost board
    2. No OT kit.
  • Jan 13, 2010, 08:56 AM
    HVACmike

    OK are the 10kw HKR-10 the sames as all the others? I may call the tech to come take a look. When in defrost the electric strips don't come on it just blows cold then. When in heat pump mode it don't blow warm it blows like cool air. Its warm but not.
  • Jan 13, 2010, 09:52 AM
    KISS

    I think you failed to mention whether the heat strips even work in say Aux or Em heat mode. Do they?

    Does the reversing valve change state in defrost?

    Does it have the optional outdoor temperature sensing kit?

    Do you need it in your climate?
  • Jan 13, 2010, 01:37 PM
    KISS

    Blowing cold air is a sign that the reversing valve is working.

    The lower the outdoor temp, the less heat you can move and the colder the air.

    First place to look is the heat strips themselves.
  • Jan 13, 2010, 05:53 PM
    HVACmike

    OK, I will probably call the tech since the unit is still under warranty.
  • Jan 13, 2010, 05:54 PM
    HVACmike
    I have not tried the aux or them setting (what ever the tstat has) but I will. It dose not have a outdoor tstat. It gets in the teens to the 10*F-12*F and I still hear the unit running!