    Electrical transfer switch
    I have a 2 pole 60 amp Manuel transfer switch. I am installing a 2 pole 60 amp breaker in my main panel with #6 wire ( 2 hots and a neutral plus ground) to feed the 2 pole 60 amp transfer switch. From the main lugs on the 2 pole 60 amp transfer switch I am feeding a sub panel with #6 wire ( 2 hots and a neutral plus ground) . In the sub panel I will have 8 ckt breakers that will be feeding various appliances (Watts will not exceed 7000). In the garage I will install a 30 Amp 240 volt Generator power cord inlet box that I will plug my portable gas Generator into with a 30 amp 240 volt cord. From the 30 amp inlet box I will be installing #10 wires ( 2 hots and a neutral plus ground) to the 60 amp 2 pole manual transfer switch.
    My question is this - The transfer switch consists of two 2 pole 60 amp breakers that can not be in the on position at the same time, one of the 2 pole 60 amp breakers is going to have the # 6 wire from my main panel the other 2 pole 60 amp breaker is going to have the # 10 wire from the generator inlet box, can I have the #10 wire feed to the 60 amp breaker or is it a violation? I can't swap out one of the 2 pole 60 breakers with a 2 pole 30 breaker because that is how the transfer switch is built. The # 10 wire is carrying power that is being made from the generator then going to the 2 pole 60 amp breaker so the 60 amp breaker is not protecting the #10 wire it is protecting the 8 ckt breakers in the sub panel. So will there be any violations with the #10 wire on the 60 amp breaker??
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Apr 16, 2010, 03:51 PM
    Does your generator have a breaker on it?
    wolfsden's Avatar
    wolfsden Posts: 2, Reputation: 1
    New Member
     
    #3

    Apr 16, 2010, 04:52 PM
    Quote Originally Posted by Missouri Bound View Post
    Does your generator have a breaker on it?
    Not sure yet I will find out and let you know.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #4

    Apr 16, 2010, 05:09 PM
    Some do. And if your generator has a 30 Amp breaker, you should be OK with the 10 ga. Wire. But no way can you use it with 60 amp circuit protection. It's not safe.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Apr 17, 2010, 04:01 AM
    MB is correct, either the genset needs to have a 30 amp breaker to protect that output, or before the input outlet there needs to be a 30 amp breaker to properly protect the #10 wire feeding the 60 amp breaker in your transfer panel.

    I am sure the genset will have a breaker.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Transfer Switch [ 2 Answers ]

How do I wire a tranfur switch for a portable 6300 watt generator coming from the Main panal to the tran tranfur switch do I need a subpanal to also can you give me A diagram also For this I would bring power from a 60 amp breaker in main panal I only want to run afew things...

Generator transfer switch [ 1 Answers ]

How difficult is it to install a generator transfer switch? It's pre-wired, doesn't look too Difficult. Is there anything I should look out for? The only thing I'm not sure of is it comes with two 15-amp 1-pole breakers, two 20-amp 1-pole breakers, and one 2-pole 20 amp breaker. How do I tell the...

Installing A Transfer Switch [ 3 Answers ]

I have a 30KW 3 phase generator I purchased from government surplus. After repairing the generator it runs fine and I will only be using 2 of the phases. Now my question. I have a new Cutler-Hamer model DT224URK-NPS 200 amp transfer switch which I have mounted above where my service enters my home....

Transfer Switch [ 3 Answers ]

Ok I am looking to add a transfer switch so I can run my generator when the power is out. I have always been told that my transfer switch needs to be rated higher then my generator's output. The problem is my generator has two output rating stated. In other words, a constance rating of 5,550 kw...

Transfer switch [ 6 Answers ]

I’ve recently purchased a Guardian 13kw standby generator with a transfer switch and load center panel. I have a couple of questions 1. The transfer panel had a total of 205 amps through 12 various breakers in it, can I replace some of them as long as I don’t go over the original 205 amps and use...


View more questions Search