        Electrical whip?
       
                  
        Greetings, I am connecting an electric heater in my garage that requires #6 gauge wire on a 60 amp double pole breaker. I want to use a whip from the disconnect to the heater, which is a distance of about 4 ft simply for the flexibility. My problem is that I can't find a 6 gauge whip. Are these available or illegal for this application? Could I make my own or should I just take the more difficult route and do it all with metal conduit like the rest of the run. I am using 1" emt with 2 wires and a ground for the whole run from the panel to the disconnect.  I thank you in advance for your reply.
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Oct 6, 2009, 03:01 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I would Make a whip.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Electrical & Lighting Expert |  | 
 
                  
                      Oct 6, 2009, 04:35 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by nick jr    My problem is that i can't find a 6 gauge whip. 
	
		
			
			
				
					  Originally Posted by Stratmando   I would Make a whip. I agree.  
Not everything comes pre-packaged at Home Depot. :rolleyes:
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Oct 6, 2009, 07:14 PM
                  
                 |  |  
  
    | 
        
        
        
       
        
        Electrical whip
       
                  
        Can I use a #8 gauge wire electrical whip with an electric garage heater rated at 55 amps? All the rest of the wiring is #6 gauge on a 60 amp breaker. It appears that the largest "pre packaged" whip I can find is #8 gauge wire. I need only a 4ft. Whip. Will this present any safety issues or danger? If need be I will just rewire the 8 gauge whip with 6 gauge wire.  Any comments, observations, questions or analysis would be greatly appreciated. Thank you in advance! 
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Electrical & Lighting Expert |  | 
 
                  
                      Oct 6, 2009, 07:19 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Just get all the parts you need and make it. That is what we do.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Oct 6, 2009, 07:28 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by stanfortyman   Sorry, not familiar with inner workings. First time user of this type forum. My apologies
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Oct 6, 2009, 08:27 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        <threads merged>
 
 PS: Nick
 
 "Answering this question" should be read as "Reply to this question"
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Oct 7, 2009, 02:51 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        To answer your original question, no, #8 wire cannot be used to carry 55 amps.
 Do as Stan mentions, make up your own whip using flexible metal conduit, the proper connectors, and the two #6 for the 240 volts and one #10 for the equipment ground.
 
 What type of wiring method was used for the feeder?
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Oct 7, 2009, 04:49 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I used 6 gauge romex on a 60 amp, 2 pole breaker concealed in the wall from the panel to to a junction box in the garage. I then used 6 gauge THHN from the junction box to the 60 amp disconnect. I now need the whip. One further question. It now seems as though I can only find 3/4" flexible conduit. Would that be acceptable since I used 1-1/4" emt for the rest of the run?
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Oct 7, 2009, 05:11 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        3/4 or 1" is fine, don't skimp on length.(Not pulled tight).
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Improvement & Construction Expert |  | 
 
                  
                      Oct 7, 2009, 05:40 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        OK gentlemen, what's a whip in Sparky talk please?
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Uber Member |  | 
 
                  
                      Oct 7, 2009, 05:57 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        A short section of raceway, flex, sealtite, even MC cable etc. with wires and connectors, usually used to change from a hard raceway method to connect to a device or appliance that needs flexibility, or the electrician is too lazy to finish the hard pipe method to the unit.
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Home Improvement & Construction Expert |  | 
 
                  
                      Oct 7, 2009, 10:10 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Thanks  TK.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Oct 7, 2009, 12:51 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Thanks gentlemen. You all have been very helpful! 
     |  
    |  |  
 
 
 
  