Unless your friend is a licensed qualified electrician, do not take any advice from him/her.
	
		
			
			
				
					
 Originally Posted by 
brian9393
					 
				 
				 some one that is a friend was looking at how many 20 amp  were in the box and said to me that my pannel box would not pass code because it has 750 amps  in breakers
			
		 
	 
 Adding up the amp ratings of all the circuit breakers in any panel means absolutely nothing.
Can you explain what your trying to do?
The 200 amp rating of the system you have was determined, or should have been,by performing load calculations, and should have some reserve ampacity for future load. 
Any idea of the new load? Has anyone done the calcs to see if your panel or service has the capacity to add load?