Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   3 way switch on 14/2? (https://www.askmehelpdesk.com/showthread.php?t=206660)

  • Apr 16, 2008, 06:46 PM
    dennypower
    3 way switch on 14/2?
    I have 14/2 on both ends of 2- 3 way swtiches. Does anyone know of a way to wire these switches without changing it out to 14-3? THANK YOU!
  • Apr 16, 2008, 06:54 PM
    Stratmando
    Have the 14-2 be the travellers. Then hook lights to closest 3 way, The Black/(light wire) goes to common on this three way, and hook up the lights neutral to neutral in box.
    Now you need to get a constant hot to the other 3 way common screw.
  • Apr 16, 2008, 07:02 PM
    stanfortyman
    There is NO Legal or safe way to make a 3-way work with only a "2-wire" between the switches.
    You CANNOT have the neutral come from one box and the hot from another.

    What does this mean?:
    Quote:

    I have 14/2 on both ends of 2- 3 way swtiches.
  • Apr 16, 2008, 07:11 PM
    MOWERMAN2468
    No.
  • Jul 11, 2010, 05:50 PM
    rygags
    Comment on Stratmando's post
    This does not make any sense! Please explain.
  • Apr 12, 2011, 10:24 AM
    baseball239
    Had a so called electrician come out and do some wiring for me for 2 3 way switches. He did not use 14/3. what he did was this, a total of 5 wires, 2 switch legs ( for two separate lights) and then 3 14/2 lines from one box over to the other box. I have tried to call hm out to redo this correctly with 14/3 but has not returned my calls, any way to make this work so I can finish my kitchen up?
  • Apr 12, 2011, 10:43 AM
    Stratmando

    Yes, can you provide some type of diagram showing the boxes involved and the wires between each of those boxes?
  • Apr 12, 2011, 11:00 AM
    baseball239
    I'm sure I can draw up something.
    How do I get this to you?

    Again thank you for your help
  • Apr 12, 2011, 11:22 AM
    Stratmando

    If you can draw it up, and scan it, then when you reply, attach the image by clicking on the mountain/sun Icon, it should show up.
    Or take a picture of your drawing, then attach the photo(s)
  • Apr 12, 2011, 02:30 PM
    baseball239
    1 Attachment(s)
    Here you go! Not the best but hope it makes sense!

    Again thank you for your help
  • Apr 12, 2011, 02:36 PM
    baseball239
    I know just enough about eletrical to get me in trouble.
    But it seems it should have been 1 14/2 wire going from one box to the next. Then instead of the other 2 14/2 wires they should have been 14/3, seems like I need to try and get another 14/2 pulled box to box or rip all drywall out and redo it the correct way.
  • Apr 12, 2011, 02:53 PM
    Stratmando

    Identify the 3 pairs of 14-2(different colored tape, numbers or letters)
    Then hook #1 14-2 to the same colored screws on each end of the cable.
    Then hook 2 more 3 ways on each end of cable 2, These 2 pairs are your travellers.
    The 3rd cable will connect to the power from the receptacle on the bottom box and the black will also need to have 2 short pigtails(black wires), each pigtail will connect to the common on each of the 3 ways. You are done with the bottom box. This was the "Hot End" of the 3 ways.
    Now back to the Top Box in the Picture, Connect the whites from the lights to the white on cable #3, And the each black from the 2 sets of lights connects the common of each 3 way(dark screw), this is the "Switched End. The black from cable 3 will get capped off, or that black and white and a ground, can be run to an additional receptacle.
  • Apr 12, 2011, 02:56 PM
    Stratmando

    I see you posted and left, while I was writing, hope you didn't rip the walls out. Maybe 14-2 is what was available.
    It will work, I will see if I can get a chance to draw this out. Have to go now. Good Luck.
  • Apr 12, 2011, 03:26 PM
    baseball239
    No I haven't ripped the walls out yet! But I will try what you wrote. A drawing would be great if you can.

    Again thank you for your help

    Don
  • Apr 12, 2011, 06:51 PM
    Stratmando

    Trying to get you the drawing, It says I have to accept scripted windows, I do and it still won't do squat?
  • Apr 13, 2011, 08:48 AM
    Stratmando

    [IMG]C:\Users\stratmando\Pictures\4-12-2011 9;44;58 PM14-2,3way.JPG[/IMG]
  • Apr 13, 2011, 10:22 AM
    baseball239
    Little confused stratmando. Wire #1 both white and black go to same colored screws? On one switch?
  • Apr 13, 2011, 10:35 AM
    baseball239
    Whatever u posted I can't open
  • Apr 13, 2011, 11:57 AM
    hkstroud
    1 Attachment(s)

    This is what Strat is telling you do do. It will work but I'm not sure that it is legal. Plus that's a lot of wires in one box.
  • Apr 13, 2011, 12:29 PM
    Stratmando

    HK, can you tell me how to post a picture, I had it in electrical, it has been moved to forums, I want to post a scanned image. Thanks
    Why wouldn't it be Legal?
    HK, here is a link to my problem:
    https://www.askmehelpdesk.com/forum-...es-570037.html Thanks
    All the Grounds get tied together, we left this out thinking it is understood, if not they need to be connected.
  • Apr 13, 2011, 12:47 PM
    baseball239
    Finally got the image thanks Stratmando. Now that I can see it visually I understand it better.
    Thanks again, I will try this out in the morning, And yes Grounds are all connected together ahaha!

    Thanks Again for your help!
    Will let you know if I got it to work!
    Shouldn't be a problem though!!
  • Apr 13, 2011, 12:49 PM
    baseball239
    Thank you too HK!! I really appreciate everything both of you have showed me
  • Apr 13, 2011, 01:09 PM
    Stratmando

    The Image is from Hk, It seems like for me to get to post an image will a long time at this rate.
    Someone has to be able to answer my question on not being able to post images?
    You will likely have it wired before I get an answer? Take care, keep us posted.
  • Apr 13, 2011, 01:21 PM
    baseball239
    I will keep you both posted. Yea I just realized the image was from HK. Thank you Both
  • Apr 13, 2011, 05:47 PM
    hkstroud

    Strat,

    As I'm sure you know, an ac voltage on one conductor will induce a small voltage in another conductor in proximity. Therefore, the need to have the neutral in the same cable as the hot conductor. Since the current in the neutral is traveling in the opposite direction it induces an opposite voltage. The two voltages cancel each other.


    When 3-wire cable is used between two 3-way switches, two of the wires are the travelers and the 3rd is either a neutral or a switched leg. Like the neutral, current on the switched leg is moving in the opposite direction, the two induced voltages cancel each other out.

    If the travelers are in one cable and the switched leg is in another, the traveler being used will induce a small voltage in the traveler not being used. The switch leg will induce a voltage in the other wire in the other cable.

    In the situation described I assume that the wiring has been done and the wall closed up. The induced voltages are very small and given the situation described I personally wouldn't worry about it. I do not think, however it meets code. If the person that did the wiring was an electrician, I don't think I would hire him again. That is unless TK or Stan comes along and tells me I am wrong about it not meeting code.


    ________________________________________________


    (From the Ask Me Help File)

    How do I add pictures and other file types to my post?

    A. "Attach" files (including pictures) from your computer. This method puts the attached file below the text of the post.

    1. Click on an Ask or Answer button to ask or answer a question
    2. Compose your question or answer in the window.
    3. Under the window where you composed your question or answer is a section called Additional Options.
    4. Click on the Manage Attachments button: a pop-up dialog will open. NOTE: The Manage Attachments dialog lists the maximum sizes of the various types of files that may be attached.
    5. Click the Browse button to navigate to the image on your computer and double click the file on your computer: this will return you to the dialog window.
    6. Click the Upload button.
    7. Click the link to close the dialog window OR repeat numbers 5 & 6 to attach another image.

    B. "Embed" image(s) from the internet. This method inserts an image wherever you wish within the text of your post.

    1. Click the Insert Image icon https://www.askmehelpdesk.com/member...nsertimage.jpg above the posting window: A pop-up asking for the URL will open.
    2. Enter the URL of the image in the field then click the OK button.
    __________________________________________________

    If you are like me and use the "Old Skin" the "Additional Options" button is the "Go Advanced" button. When using the "Attach File" method, the image is uploaded from you computer to the AMHD web site and then attached to the end of your post.

    If you want to embed an image directly in your post, like this
    https://www.askmehelpdesk.com/member...e658-strat.jpg

    The image must first be uploaded to the internet somewhere. It can be anywhere as long as you can provide the URL.

    To upload am image to AMHD, click on "My Profile", click on "Pictures & Albums", click on "My Pictures" , click on "Upload Pictures".

    To embed the image in you post, first go to "My Profile, Pictures & Albums, My Pictures" left click on the image and copy the URL. Then when making you post, click on the image insert button https://www.askmehelpdesk.com/member...nsertimage.jpg and provide the URL.

    PS
    There is a size limitation to posting pictures or images. Best to convert to JPEG before uploading.
  • Apr 14, 2011, 02:46 AM
    tkrussell

    I see no problem with the wiring, while not how it is normally done.

    No different that a two wire switch loop.
  • Apr 15, 2011, 10:48 AM
    baseball239
    Strat and HK, The diagram works, however, I am only getting 84 volts to one light, tested at the box 120v but up to the box only 84v. Thank you again for your help
  • Apr 15, 2011, 11:12 AM
    tkrussell

    We will need to know which light you have 84 volts at.

    Seems you have something spliced in series.
  • Apr 15, 2011, 11:43 AM
    baseball239
    Looking at the diagram it is light on right of diagram
    Again thanks for your help
  • Apr 15, 2011, 04:48 PM
    Stratmando

    I would guess a neutral connection?
    Plug an extension cord into a known good outlet with 120 Volts on it, bring to your light and use the cords neutral as a reference.
    If you use the Neutral on the cord and the hot at the light and it is 84 volts, it is the Hot and may be one of the switches or a connection.
    If it is now 120 volts, the neutral is the problem, and check the whites in both boxes, Not the whites that have been taped with black tape on the switches.
  • Apr 18, 2011, 02:00 PM
    hkstroud
    1 Attachment(s)

    There are quite a lot of wires there. It is possible you mis-wired a white wire. Some whites wires are neutrals and some are being used as hot conductors.

    I have changed the color of the whites that are being used as hot conductors to purple to make the drawing easier to read.

  • All times are GMT -7. The time now is 11:19 PM.