  • Jan 25, 2009, 08:19 AM
    IfixIt
    Quote:

    Originally Posted by Stratmando View Post
    In that case, I would forget about the switch, leave on high, and get a wall Speed Control.

    Thank you for your suggestion. It's a great fix around and I will do just that if this second switch doesn't work. The point is, however, to let other users that run into the same problem know about these replacement switches that HD sell for their exclusive Hampton Bay fans.
  • Jan 25, 2009, 08:24 AM
    Stratmando

    I do know it can be a pain finding correct switch, being stuck in High is best case.
  • Jan 25, 2009, 08:25 AM
    IfixIt
    Quote:

    Originally Posted by IfixIt View Post
    Thank you for your suggestion. It's a great fix around and I will do just that if this second switch doesn't work. The point is, however, to let other users that run into the same problem know about these replacement switches that HD sell for their exclusive Hampton Bay fans.

    Sorry! My statement should read:... the GE replacement switches that Home Depot sell for their exclusive Hampoton Bay fans are not interchangeable and do not work.
  • Jan 25, 2009, 02:49 PM
    IfixIt
    Follow-up to my previous posts. OK... as I said before the first 4 wire 3 speed fan switch did not work and had to return it. I then got the other switch they had in stock which is a Westinghouse #77020 3-4 wire 3 speed switch and this one did the trick. It works just fine.

    Here is what you must do:
    1. Once you have access to the switch and before you pull the wires make sure to write down the color and position of the wires like this: #1=gray, #2=brown, #3=black and #L=purple. Also, do not make the mistake of cutting the wires; there is no need to cut the wires.

    2. To pull the wires from the old switch, insert a straightened out paper clip into the wire terminal and push down the spring while you pull the wire.

    3. Rewire the new switch with the color/position wires as the old switch

    If if your fan is stuck in high speed like in my case and you cant find the correct switch; the other work around as suggested by Stratmando is to opt to install a wall speed control also known as a dimmer switch.
  • Jan 26, 2009, 01:11 PM
    ceilingfanrepair

    First of all, when you say it was stuck on high, what happened when you attempted to switch it to a different speed, did it click?

    Ceiling fan pull chain replacement and repair - Ceiling Fans N More
  • Jan 26, 2009, 03:38 PM
    IfixIt
    [QUOTE=ceilingfanrepair;1509572]First of all, when you say it was stuck on high, what happened when you attempted to switch it to a different speed, did it click?

    I said it was stuck on high because the pull chain broke off inside the switch and luckily the fan was running in high speed. I could not switch it to different speeds because there was no chain to pull.
  • Jan 26, 2009, 04:24 PM
    Stratmando

    Some can be dissassembled by pressing 2 or 3plastic clips, can be reattached, a little tricky.
    Wouldn't suggest repairing the rivited ones unless, able to do safely.

    CeilingFans Link is very helpful for finding a replacement switch.
  • Jan 26, 2009, 08:43 PM
    ceilingfanrepair

    What make is the fan?
  • Oct 25, 2009, 09:36 AM
    jdmclv
    I am also needing to replace the switch due to a broken chain. I tried a similar switch from home depot and it did not accommodate for the 'off' position which I must have as there is no wall switch for the fan (it is wired directly into the breaker box). The original switch is a dual layer switch that I disassembled to see how it works. One layer controls the on & off with the line wire and in the on position it gives power to the other layer for the 3 speed control. Mine also has the black capacitor box that I was able to test by straight wiring each speed position individually. I have pretty much figured out that I must obtain this same particular type of switch in order for the fan to be controlled properly. Home depot basically only sells a 4 wire switch that does not provide for the 'off' position and an 8 wire switch which is dual layer that fuctions entirely different (although it it shaped exactly the same as my broken one). So I'm basically still at square one with the switch and have decided to straight wire the low speed setting and use the breaker box for on & off until I find the right switch (hopefully by next spring).
  • Oct 25, 2009, 10:07 AM
    Stratmando

    If you cannot find correct switch, maybe wire for Full Speed, and use a Fan Control?
    You may find additional info on one of the last 9 pages.
  • Nov 2, 2009, 10:17 PM
    ceilingfanrepair

    What make is the fan?
  • Feb 2, 2010, 12:27 PM
    rmavriam
    A hunter fan
  • Feb 2, 2010, 12:27 PM
    rmavriam
    A hunter fan
  • Feb 2, 2010, 12:27 PM
    rmavriam
    A hunter fan
  • Feb 2, 2010, 12:27 PM
    rmavriam
    A hunter fan
  • Feb 2, 2010, 01:21 PM
    Stratmando

    Let me see if I get this right, You have a Hunter Fan? If so, what colors do you have?
  • Feb 2, 2010, 10:50 PM
    ceilingfanrepair

    What about your Hunter fan?
  • Jun 5, 2010, 06:50 AM
    ILBARONE
    This is an old question; However I will endeavor an update; First the
    3 speed 4 wire switch wiring connections are always the Power to 'L' Which is the BLACK WIRE Silver/grey #1,Brown #2,Purple #3..
    The high speed wire is usually the SILVER # 1... A simple test would be connect the Black (Line wire) to #1 Silver directly w/o switch should make fan fly. Check each wire same way note results. As fragile as the pull chain switch is I always turn on/off from a wall switch. Leaving the pull chain on medium will result in lesser strain on pull chain. SECONDARY cause of malfunction is the Capacitor Module
    Which connects to switch. This part has to be ordered from Manufacturer.. Most electricians do not carry them except they may utilize spare parts from broken fans etc.
    Quote:

    Originally Posted by boojumm View Post
    did not work as the chain broke off inside. The wires were in this order. Purple to the "L" connector, Black to the "1" connector, Brown to the "2" connector, and Grey to the "3" connector. The new switch is identical to the old one from the outside... I guess it could be different inside. I obtained it from Home Depot and the staff there seemed knowledgeable and pointed me to this one. When I thought it was defective, I returned it and purchased another at Lowe's... Same problem.

  • Jun 5, 2010, 05:29 PM
    Kenadale
    The fan I have is about 20 years old. The neck of the switch broke, but the switch still worked. I did what most everyone else did, went to HD and Lowe's for a 4 wire, 3 speed switch and installed it. The fan would not work! I uesed my OHM meter to check and compare the switch configuration of the old switch with the new switch. The were very different. The original switch was a KTE 308-A. Using my meter I measured between L and each of the other three connections( 1,2,3) for each position of the chain pull. The following are the results of the test.

    Position L / 1 L / 2 L / 3
    1 ON ON OFF
    2 ON ON ON
    3 OFF ON ON
    4 ON OFF ON

    This is the switch configuration that I need. It may be time to replace the fan.
  • Jun 22, 2010, 12:15 AM
    ceilingfanrepair
    Quote:

    Originally Posted by ILBARONE View Post
    This is an old question; However I will endeavor an update; First the
    3 speed 4 wire switch wiring connections are always the Power to 'L' Which is the BLACK WIRE Silver/grey #1,Brown #2,Purple #3..
    The high speed wire is usually the SILVER # 1... A simple test would be connect the Black (Line wire) to #1 Silver directly w/o switch should make fan fly. Check each wire same way note results. As fragile as the pull chain switch is I always turn on/off from a wall switch. Leaving the pull chain on medium will result in lesser strain on pull chain. SECONDARY cause of malfunction is the Capacitor Module
    which connects to switch. This part has to be ordered from Manufacturer.. Most electricians do not carry them except they may utilize spare parts from broken fans etc.

    1. High is not always silver in many fans
    2. Don't go randomly connecting wires, you may fry something
    3. Leaving fans on medium is silly. The speed switch is there for a reason
    4. Capacitor malfuction is actually more common than pullchain malfunction, and they can be ordered online.
  • Jun 22, 2010, 12:15 AM
    ceilingfanrepair
    Quote:

    Originally Posted by Kenadale View Post
    The fan I have is about 20 years old. The neck of the switch broke, but the switch still worked. I did what most everyone else did, went to HD and Lowes for a 4 wire, 3 speed switch and installed it. The fan would not work! I uesed my OHM meter to check and compare the switch configuration of the old switch with the new switch. The were very different. The original switch was a KTE 308-A. Using my meter I measured between L and each of the other three connections( 1,2,3) for each position of the chain pull. The following are the results of the test.

    Position L / 1 L / 2 L / 3
    1 ON ON OFF
    2 ON ON ON
    3 OFF ON ON
    4 ON OFF ON

    This is the switch configuration that I need. It may be time to replace the fan.

    CeilingFanParts.com Home should have that switch for you.

    Ceiling fan pullchain replacement and repair - Ceiling Fans N More
  • Aug 9, 2010, 09:23 AM
    Oldsman
    Contact SWITCHCO. Only correct answer! After searching these forums and many others, I finally broke down and called the Texas based company and a few days later and simple a description of and previous wiring layout for my fan, and POOF my fan once again works beautifully.

    Thanks so much Switchco.
  • Aug 9, 2010, 09:27 AM
    Oldsman

    The ONLY correct answer is to call, email, fax SWITCHCO.

    After searching this and many other forums, I decided to call switchco and after a brief description of my fan and its previous wiring scheme, a few days later and POOF my fan works beautifully once again.

    Thanks so much Switchco
  • Aug 13, 2010, 05:50 PM
    ceilingfanrepair

    If the manufacturer of the fan is still in business, I recommend calling them first. If not, I recommend calling CeilingFanParts.com Home
  • Aug 13, 2010, 06:45 PM
    Stratmando

    Both are the same site.
  • Aug 13, 2010, 07:14 PM
    ceilingfanrepair

    I know.
  • Aug 15, 2010, 10:28 AM
    cycloneracer
    Here is what the problem is boys when you replace your original 4wire/3 speed switch with a Home Depot 4 wire/3 speed switch... I'm an electronics engineer and fell into the same trap you guys did. I figured it out though after burning 3 hours of time. The damn 4wire/3speed switch Home Dopot sales (and I may add the only one they sell) has a different internal switching logic than the original! Inside the switch is a electrical commutator that has the fan speed wiring logic on it for your particular fan. The switch HD sales even though it has the Same numbers on it has different switch logic! So what I did was remove the top half of my old switch by releasing the clips on the side and installed it on the new bottom half of the HD switch. Since the pull chain part was bad on mine that fixed it. That was a stumper for a while though!
  • Aug 15, 2010, 10:42 AM
    Stratmando

    Was the trick preloading the spring a little more?
  • Aug 15, 2010, 07:56 PM
    cycloneracer

    No. I just swapped the top half of my bad switch and installed it on the bottom half of the new one. In other words, I used the mechanical (pull chain) part of the new switch and installed my electrical part (top half of switch) on that to make one whole switch again. And it worked just fine. Spring tension was OK on my electrical part of the switch.
  • Aug 16, 2010, 06:20 AM
    Stratmando

    I've repaired many switches, easier than finding a replacement, actually in most cases, it was just a broken chain, found lack of preloading spring enough is learned quickly.
    Here is the Logic for many fan switches:

    CeilingFanParts.com - Switchco Products - Pull Chain Switches
  • Aug 22, 2010, 05:07 PM
    kevin39

    Here is a possible solution.
    I have a Regency, Professional Series Fan
    The wiring on the switch is 3=Purple, L = Black, 2 = Brown and 1 = Gray, with 5 wires coming out of the capacitor.
    If you have this wiring sequence, call SWITHCO at 800-365-4548 and order Part No: A09. It worked for me. If the wiring is different, call anyway with the wiring sequence and they may be alble to help you out. Good Luck.
  • Aug 24, 2010, 04:51 AM
    Oldsman

    They did a wonderful job for me, I called them, gave a description of my fan make and model unknown, anyway, told them how it was wired originally and they didn't even have to look it up, the nice lady knew her stuff and a few days later, my fan worked perfectly.
  • Sep 25, 2010, 12:20 AM
    Logitech702
    I replaced a 4 wire Unit (3-Speed Fan Switch) on 4/22/2010 Earth Day because the old one that it was on my ceiling fan started to sparked fire. So what I did, I went to Lowe's and bought a new 4 wire Unit (3-Speed Fan Switch) so I replaced it and it didn't work when I installed the new 4 wire Unit (3-Speed Fan Switch). So what I did, I used a # 18 solid wire and hooked them on the 4 wire Unit (3-Speed Fan Switch) and it started working again. (:
  • Sep 25, 2010, 01:36 PM
    cycloneracer

    You got to watch out on what replacement switch you are buying. What I noticed is there are at least two different types of 4 wire switches at Home Depot. They look the same from the outside except for the color of the plastic, but what the different is the pattern they electrically switch the four wires which is not the same. There is a logic tumbler inside the switch and that is what is different between the two types. If you install the wrong switch, the fan will not work or just hum in one of the speeds. So if this happens buy the other switch.
  • Sep 29, 2010, 05:14 PM
    Logitech702
    ↑1= Yellow
    ←2= Purple
    ↓3= Black
    →L= Orange
  • Sep 29, 2010, 06:38 PM
    Stratmando

    This is from Ceiling Fans Earlier post:

    L - Black, 1 - Grey, 2 - Brown, 3 - Purple
    L - Orange, 1 - Black, 2 - Yellow, 3 - Purple
    L - Black, 1 - Grey, 2 - Brown, 3 - Green
    L - Grey, 1 - Yellow, 2 - Purple, 3 - Black
    L - White, 1- Black, 2 - Blue, 3 - Yellow
  • Dec 27, 2010, 01:39 PM
    MN_Jack76
    I know this is an old post but maybe I can help someone who has the same question. 3 speed pull chain switches are not universal. Fans have different wiring, different color codes and most importantly different "cams" inside the switch. Just because a switch looks similar, It is probably different inside. Here is a company I found that you can send your switch to. http://www.fanmanlighting.com/shop/pc/viewCategories.asp?idCategory=69 You will have to send the switch to them and they will have to break the switch open to identify it and will hopefully have a replacement.
  • Mar 28, 2011, 07:47 PM
    ricanet
    If you look up into the fan housing and see a rectangular black device with three wires coming out of it, you must get a 'Dual Capacitor' switch. The power wire (black)goes on #3; the wire from the fan direction switch (purple) goes on the 'L' terminal; the two wires from the rectangular device go onto (yellow)#1 and (Blue)#2.
  • Mar 29, 2011, 06:18 AM
    rdsatkaycee
    This has been going on so long, and don't know I I posted the solution for this or not, but Home Depot carries two switches; one works and the other one doesn't. I at one time had written down the number of which one works. Try one, if it works great, if it doesn't, take it back and get the other one.
  • Aug 11, 2012, 11:37 AM
    jcorbat
    The best way to figure out switch compatibility is using a continuity meter and paper clips:
    http://www.dansfancity.com/techhelp/parts/testswitch.htm

    Test the old switch and then compare to the operation of the replacements. Make a grid on Excel to keep track:

    Defond E72989
    L+1 L+2 L+3 1+2 1+3 2+3
    Pos1 y n y n y n
    Pos2 y y n y n n
    Pos3 y y y y y y
    Pos4 n y y n n y
    Pos1 y n y n y n

    Westinghouse 77020
    L+1 L+2 L+3 1+2 1+3 2+3
    Pos1 y n y n y n
    Pos2 y y n y n n
    Pos3 y y y y y y
    Pos4 n y y n n y
    Pos1 y n y n y n


    Westinghouse 77021
    L+1 L+2 L+3 1+2 1+3 2+3
    Pos1 n n y n n n
    Pos2 n n n n n n
    Pos3 y n n n n n
    Pos4 n y n n n n
    Pos1 n n y n n n