  • Nov 22, 2013, 11:59 AM
    rr6
    Hi Stan-40, I finally got back into the 100 amp main panel I'm pulling off for my 2-pole 50-amp feebdack main.

    In this 20 year old Square D box, the ground bus bar is isolated from the metal box by plastic. So I will leave my on the few neutrals that are there. I guess.

    I forgot to check and see if there is only 1 neural per hole on the neutral bar, from 20 years ago when I installed it. Probably is since I have not used on the breaker slots.

    I go the retaining g clip installed on the 2-pole feed-back main in the sub-panel. Thx again for that excellent tip!

    Another question if your still here, is the leads and neutral to sub-panel are #6 and I ran a #8 ground wire to the ground rod outside cabin for the sub-panel.

    Seems I recall two suggestions elswhere in my readings;

    1) I should use as large or larger than the leads, ground wire to the ground rod,

    2) I should have installed two ground rods?

    I put the ground rod in on 8 or 10ft ground rod in on a 45 degree slant and was short if getting it all the way in by about 2 or 2.5 ft.

    Also I installed the rod so that its actually under the house, so it may get less moisture from rain fall ergo less good grounding.

    Thx for any advice.
    Quote:

    Originally Posted by stanfortyman View Post
    If there are neutrals actually on an add-on ground bar, screwed directly to the back of the panel box, I would definitely move them to a neutral bar.
    The panel box itself cannot be a path for neutral current.

  • Nov 22, 2013, 12:01 PM
    rr6
    Hi Stan-40, I finally got back into the 100 amp main panel I'm pulling off for my 2-pole 50-amp feebdack main.

    In this 20 year old Square D box, the ground bus bar is isolated from the metal box by plastic. So I will leave my on the few neutrals that are there. I guess.

    I forgot to check and see if there is only 1 neural per hole on the neutral bar, from 20 years ago when I installed it. Probably is since I have not used on the breaker slots.

    I go the retaining g clip installed on the 2-pole feed-back main in the sub-panel. Thx again for that excellent tip!

    Another question if your still here, is the leads and neutral to sub-panel are #6 and I ran a #8 ground wire to the ground rod outside cabin for the sub-panel.

    Seems I recall two suggestions elswhere in my readings;

    1) I should use as large or larger than the leads, ground wire to the ground rod,

    2) I should have installed two ground rods?

    I put the ground rod in on 8 or 10ft in on a 45 degree slant and was short if getting it all the way in by about 2 or 2.5 ft.

    Also I installed the rod so that its actually in ground under the cabin, so it may get less moisture from rain fall ergo less good grounding.

    Thx for any advice. Next I figure reepticles, wiring lighting.
    Quote:

    Originally Posted by stanfortyman View Post
    If there are neutrals actually on an add-on ground bar, screwed directly to the back of the panel box, I would definitely move them to a neutral bar.
    The panel box itself cannot be a path for neutral current.