Originally Posted by
hkstroud
What Strat is suggesting is that you plug in an extension cord, make sure that it is working by doing a voltage check between hot and neutral.
Take extension cord to bath room. Do a voltage check between the hot of the extension cord and the neutral of the bath outlet. If your meter shows voltage, that would mean that your neutral does indeed go back to the circuit breaker panel. If it meter does not show voltage, you have a broken neutral some where. If meter does not show voltage to the neutral do a voltage check between the hot of the extension cord and the ground of the outlet. A voltage would show the outlet is at least grounded.
Do a voltage check between the hot of the outlet and the neutral of the extension cord. Do that check with the breaker on and with the breaker off. If you have voltage with breaker on and then do not have voltage with the breaker off you will have at least confirmed which breaker controls the outlet.
If you show no voltage with breaker on (assuming all other breakers are on) you will know you have a break in the cable some where.
Have you examined the exterior outlet that you have just found inoperative. Always possible that the circuit to the bath runs through that outlet and has been disconnected in the box of the exterior outlet.
Remove the circuit breaker panel cover and see if anything is connected to the unaccounted for breaker.
Let us know what voltage reading you get, not sure what they will mean but you are just looking for a clue, something to point you in some direction.
Do you have a garage or a basement? Do you have any other exterior outlets, working or non-working. Check to make sure.
Pull a couple working outlets, are the outlets wired using the "quick connect" holes in the back or are they wired using the screw terminals?
I just look back at all your post. No where do you describe the wiring at this outlet.
How many wire in outlet box?