Originally Posted by
donf
Harold,
I cannot about code editions prior to the 2008 edition. I do have a copy of the 2005 edition but that is all the way across my office and I'm just to lazy right now.
The code a minimum of 1 20 amp branch circuit to serve a bathroom, inclusive of a GFCI receptacle outlet. Yes, there can be more than one circuit. However, if there is only the one 20 amp circuit, it is not permissible to serve any other bathroom.
If there is a dedicated 20 amp circuit for the exclusive use of the receptacle outlet then you have the option to extend that circuit to another bathroom for the exclusive use of a receptacle outlet. It cannot serve any other loads but receptacles.
Are we saying the same thing?