My question regarding disconnects to a main service was simply this:
Is there a limit of total disconnects that can be in series on the load side of the main service disconnect? This question was not answered.
You have stated many times that a grounding electrode is only allowed to be bonded to the grounded conductor at the main service disconnect. Are you citing 250.24(A)(5) Load Side Grounding Connections as your basis that no other bond of the grounding conductor shall be made to a grounding electrode except at the main service disconnect?
If so please advise regarding your opinion of 250 Section III, 250.50 Grounding Electrode System which states "all grounding electrodes ...that are present at each building or structure served shall be bonded together to form a bonding electrode system" Is this not stating more than one electrode in multiple locations bonded together?
I still do not find a specific line of code that DOES NOT ALLOW more than one grounding electrode to be attached to the grounded conductor at a location distant from the service entrance, except possibly 250.24(A)(5)? Please cite it. Just reading 250.24 in totality does not answer the question... Again please cite the line of code that DOES NOT ALLOW more than one grounding electrode.
The multiple grounding electrode question is the only one still on the table between me and the "new electrician who appears very competent" and the commercial company responsible for the genset/ATS install. A schematic drawn by a P.E. for the company shows a grounding electrode at the meter service entrance connected to the grounding conductor which runs to the house and a grounding electrode at the house connected to the same grounding conductor. They both have signed off on the install. So who is right??
Can an additional grounding electrode be placed at a distant point along the grounding conductor or not. Cite the exact code line that I can show them.
P.S. I also contacted the generator dealer (CAT Olympian) and their guy said in most installations they installed their gensets they saw a grounding conductor bonding the enclosure/case/block of the genset (separate from neutral) and also a grounding electrode attached to the same point on the genset in a non separately derived genset/ATS intall.
Thanks again as always...
Huck