Originally Posted by
Missouri Bound
Rotten....I will try to address your last post as politely as I can, but I am sure you will take it as an insult. You said that you were the most qualified but you do not understand the basic ampacity of wire, or the severity of the situation. A 100 amp panel requires a a minimum of #2 wire. # 8 is rated at only 45 amps, and at that distance you should be using a 40 Amp breaker. If that is not enough, then you need to replace ALL the wire. And you should be using 4 wires, not 3. Again I suggest you hire someone more qualified than you to asses the situation.