This WHOLE thing is wrong from the get go, and for several reasons.
1) You CANNOT feed a detached structure with more than one circuit. For this purpose a multi-wire circuit is considered one circuit.
It is being proposed to run MANY circuits to this garage. NOT good.
I am still uncler if this is detached or attached. If it is attached then this does not apply.
2) Derating was brought up. For all practical purposes, over NINE CCC's (current carrying conductors) you must start to derate #12 THHN. It is involved as to why, but ten or more CCCs and you must derate to the point where you are under the "standard" 20 amps for #12.
Keep in mind, the neutral of a MWBC (multi-wire branch circuit) does not count as a CCC nor do grounds.
It is being proposed to run WAY more than nine CCCs.
For instance, if he runs ten MWBCs, for twenty circuits, this is 20 CCCs and he MUST derate those circuits to 50% of 30 amps, or 15 amps.
IF this is an attached garage, then you would have to run several smaller conduits with up to eight circuits, (even MWBCs) in each to allow each circuit to stay 20 amps.
I can understand trying to save money and using something you have on hand, but butchering a job and doing things ALL wrong is NEVER a good way to go.
If you are insistent on using the THHN you then have go the multiple conduit run route provided the garage is attached as I said.
NOT true, you need ONE ground per raceway, based on the largest circuit conductor.Quote:
Originally Posted by EPMiller
So you can have 100- #12 wires in a conduit and you would only need ONE #12 ground.