Originally Posted by stanfortyman
MR500, you DO need to run 4 wires to the shed. You will run an equipment ground and yes, this will get bonded to the panel as well and the grounding electrode conductor (ground rod wire). The neutral in the sub will be isolated (not bonded).
This is a "typical" remote sub-panel installation.
DO NOT add a neutral wire to that add-on lug. That must be used for grounds ONLY.
A neutral must go to the other bar. The grounds can go to either place.
You can get an add-on lug to connect a larger conductor to that neutral bar you know. You remove a screw and the larger lug gets mounted right to the bar.
This is the route I'd go.
Great pic BTW.