Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Appliances (https://www.askmehelpdesk.com/forumdisplay.php?f=157)
-   -   Outdoor A/C unit hums but doesn't come on (https://www.askmehelpdesk.com/showthread.php?t=105880)

  • Jul 1, 2007, 02:51 PM
    jjet555
    Outdoor A/C unit hums but doesn't come on
    I have a 2 ton century A/C unit. The outside unit will not come on, but it hums. I have determined the following:

    The air handler fan in the inside unit comes on.
    The compressor and the fan in the outdoor unit do not come on, but it hums. (I assume the compressor is not coming on... lines are not cold)
    The contactor is working (the contacts connect when energized)
    The dual run capacitor reads open (infinity) on both sides and it doesn't read any voltage after I check it with an Ohm meter, then put it on A/C volts.
    I read 2.2 ohms across the compressor leads (red and blue)
    I read 83 ohms across the 2 fan motor leads (yellow and brown)

    According to the readings, I think I have a bad capacitor. Would that be correct?

    Thanks for any help!!
  • Jul 2, 2007, 11:36 AM
    ebaines
    Sounds like a shot capacitor. I had two blow on me in the past 5 years, and both times it acted as you describe - a loud humming but the compressor fan wouldn't come on.
  • Jul 2, 2007, 08:19 PM
    hvacservicetech_07
    Do you have voltage to the contactor on the air conditioner?

  • All times are GMT -7. The time now is 07:22 AM.