PDA

View Full Version : Is # 4 awg thhn copper big enough for 100 amps


alexandertmg
Jul 26, 2012, 06:18 PM
Can I use # 4 awg thhn copper for 100 amps is it big enough ?

Lectricman
Jul 26, 2012, 06:57 PM
Use #2awg copper minimum at least in Canada, assume US to be same.

tkrussell
Jul 27, 2012, 02:35 AM
#3 THHN copper is rated 100 amps, as per Table 310.16 of the 2008 edition National Electric Code for a feeder.

If this feeder is the service entrance conductors for the service of a dwelling, you may use #4 copper.