I'm installing a whirlpool tub in my master bedroom.  The elctrical requirement is a dedicated circuit for the pump and a circuit for the heater.  Both will need to be GFCI protected.  I ran a 12/3 cable thinking I can use a double pole 20 A GFCI breaker.  However, I have heard it will not work as it cannot monitor both circuit which I don't understand why not since it's double pole.  I have not purchased the breaker since I don't want to spend the $$$ on something that will not work. Thank you for your feedback.
 KISS
Feb 5, 2008, 12:50 AM
You haven't specified the electrical requirements: e.g.
 
Heater 15.4 A  240 V  20 A GFCI Circuit breaker recommended
Pump  1/2 HP  120 V  15 A GFCI Circuit breaker recommended
 
You should also specify the distance to the breaker box.
 kimo
Feb 5, 2008, 10:07 AM
The electrical requirements are:
 
1) heater - 120 Volts 12.5 amps 
2) pump - 120 Volts 7.5 amps
 
The distance from the breaker box to the outlet is 60 feet.
 ballengerb1
Feb 5, 2008, 11:36 AM
So you are saying you ran just one 12-3 cable up to the tub, right?
 kimo
Feb 5, 2008, 11:49 AM
Yes, I only ran one 12-3 cable up to the tub.
 tkrussell
Feb 5, 2008, 11:56 AM
Then a  2 pole GFI breaker will work fine.
 KISS
Feb 5, 2008, 12:27 PM
Actually if you ran a 12-3 with ground, your probably OK with a 240 V 2 pole 20 Amp tandem  GFCI breaker if the distance is  59 feet, 3% drop at 59 feet,  and the heater load is classified as operating more than 3 hours at a time.  The pump load isn't a problem.
 
The neutral will only carry the difference current of 12.5-7.5 amps, so you won't overload the neutral.  Both circuits will trip simultaneously which would be an advantage.