  • Jun 27, 2007, 05:31 PM
    Jaysmad74
    Central A/C Unit (Goodman)Blower won't run!
    Im am a new home owner.Know nothingabout central A?C's.I went to start it up yesterday and the unit kicks on outside but the blower won't blow anything out of the ducts any idea thanks!
  • Jun 27, 2007, 05:41 PM
    hvacservicetech_07
    Well, with the power off to the furnace, remove the blower door and give the blower wheel a spin, does it spin freely?
  • Jun 27, 2007, 05:43 PM
    esquire1
    Could be the motor, capacitor, relay or door switch Is the panel on on the inside unit? Does it make any noise? You could put a jumper wire on R&G and the thermostat or inside the unit.Disconnect power first. Does anything happen?
  • Jun 27, 2007, 05:45 PM
    esquire1
    Oops. We posted same time.
  • Jun 27, 2007, 05:56 PM
    Jaysmad74
    The Blower was working fine when we where running are he couple months ago
  • Jun 27, 2007, 05:57 PM
    Jaysmad74
    Heat*
  • Jun 27, 2007, 06:00 PM
    Jaysmad74
    Was going to try running the heater,But therm. Won't go that high .
  • Jun 27, 2007, 06:16 PM
    esquire1
    Have you spun the blower wheel yet. Do you have a door switch?
  • Jun 28, 2007, 06:06 AM
    labman
    Heat usually uses a different motor winding and relay than A/C and fan on. Most quick check is fan ON. If the fan comes on, but not in A/C and auto, the problem is with the thermostat or its wiring. If the fan doesn't run on Fan ON, next check with R and G jumpered at the furnace. You must have power to the furnace including having the door switch held in. Post back with these checks.