  • Sep 9, 2007, 07:47 AM
    Brenda07
    Studor Vents
    We are installing plumbing and purchased studor vents, where and how do we install the studor vents, please help, we need a diagram if possible :)
  • Sep 9, 2007, 08:19 AM
    speedball1
    Studor Vents or AAV's(Air Admittance Valves) take the place of a regular vent through your roof. They mount downstream from the trap and perform a regular vents function. Install a upright tee between the trap and the wall stub out. Now glue in a Studor Vent and the fixture will be vented. Good luck, Tom
  • Feb 19, 2008, 08:17 AM
    captonmidnight58
    Can a studor vent be installed insde the wall
  • Feb 19, 2008, 08:58 AM
    speedball1
    Quote:

    Originally Posted by captonmidnight58
    can a studor vent be installed insde the wall

    Only if a access panel is provided.
    Since a AAV is a mechanical vent it can go bad. If it's inside a wall it can't be serviced so it's best to keep them where you can get at them. AAV's aren't allowed in some areas. Check your local codes. Good luck