Poster in E&L needs some HVAC advice also, LRA of a 5 Ton unit
This is not really practical to try to deliver 120 volts at 150 feet and have the capacity for 400 amps. Assuming the maximum load of each 200 amp service to be 80% of full rating, would mean the calculations would be based on 320 amps, or 160 amps for each service entrance.
Thanks for your answer. However we need to deliver 240 volts and not 120. Currently the wire size from the transformer pole to the secondary pole[120'] is a 1\0 al triplex.A 1\0 al triplex is also used from the secondary pole to each 200 amp service entrance at an approx. distance of 35' each. Would you believe our lights dim when our 5 ton A\C kicks on ? The utility co. will not replace the wire. I am involved in a court hearing with the CPUC on Mon. 1/14 @ 1:00 pm that involves this matter. HELP:)