    DIY Al
    Two Single Pole GFI's = one Double Pole 220v GFI?
    Hello there,

    Installing a pool motor, 220v hayward northstar two speed. Could not find a double pole 40 amp GFI, electric supply store recommended two single pole 20A GFI's sharing a neutral? Does this make sense. I have a 40amp double pole in the main feeding the sub via the sub panel lugs, looking for a min of 20a at the motor (draws 14a). I greatly appreicate your help. AL
  • Sep 11, 2007, 04:30 PM
    tkrussell
    Where do people come up with this stuff?

    Ask them to connect it that way in their home for their pool with their kids in the pool.

    Why are you looking for a 2 pole 40 amp breaker when the motor draws 14 amps at 240 volts, which will need a 20 amp breaker?

    What brand panelboard do you have?
  • Sep 11, 2007, 05:27 PM
    DIY Al
    Thanks, I knew it didn't seem correct, my panel is a siemens
  • Sep 11, 2007, 05:29 PM
    DIY Al
    Quote:

    Originally Posted by tkrussell
    Where do people come up with this stuff?

    Ask them to connect it that way in their home for their pool with their kids in the pool.

    Why are you looking for a 2 pole 40 amp breaker when the motor draws 14 amps at 240 volts, which will need a 20 amp breaker? I have a single pole 20a, I guess I would need a double though to connect via the lugs on the sub, right?

    What brand panelboard do you have?

    Siemens
  • Sep 12, 2007, 04:58 PM
    tkrussell
    I attached a page of Siemens catalog for their GFI breakers.
  • Sep 12, 2007, 05:49 PM
    DIY Al
    Quote:

    Originally Posted by tkrussell
    I attached a page of Siemens catalog for their GFI breakers.

    Thanks, OUCH! Okay perhaps I should explain the WHOLE system to make sure I do it right. Again a 40a two pole out of the main, via 8ga 3 conducter with a 10ga ground TM cable, length of run 15ft. Siemens outdoor sub panel, off the sub I will have one circuit (circuit 1)powering a on/off timer (intermatic T104), then a two speed timer (intermatic T106) a 2 amp 220 clorinator and the hayward pump 220 14amp (peak) which has 3 12ga wires coming out of the motor (red, black, white)

    Circuit #2- 15A GFI to a outdoor receptical box with a switch and duplex GFi receptical powering a 600watt 12v outdoor transformer for my 300watt 12v pool light

    So for Circuit 1 I should go with a 20A 2 pole GFI, although I can't find in the code where it needs to be a GFI for a pool pump that is hard wired (thoughts?)

    Circuit #2 a 15a GFI (can it be a regular breaker since the receptical is GFI?) Thank you for your help, DIY AL
  • Sep 12, 2007, 06:02 PM
    tkrussell
    OK, the 40 amp does not need to be a GFi, since the light and outlet already has GFI protection.

    Correct, a 240 volt pool pump motor does not need GFI protection. I was not going to mention that unless you mentioned it, always good to exceed code, but not necessary.

    Wow, someone else actually reads the code? Outstanding.