Originally Posted by
donf
Most of your questions will hinge on the manufacturer of your new tanning bed.
However, you cannot simply remove the 30 amp breaker and pop in 15 or 20 amp breakers.
The wiring between the panelboard and the timer will have to be removed if you want this done properly.
Just guessing but it sounds to me as if you have a 204V/30 Amp tanning bed?
If you do, then removing the breaker is a simple task, replacing the breaker with either 15 or 20 amp breakers is another story.
30 Amps require a 10 AWG cable. 20 amps require 12 AWG cable and 15 Amp uses 14 AWG cable.
Under no circumstances can you use 14 AWG cable in a 20 amp circuit unless the entire circuit is reduced to 15 amp. That is a fire waiting for the time to start!