    ThomasCKeat's Avatar
    ThomasCKeat Posts: 157, Reputation: 12
    Junior Member
     
    #1

    May 31, 2007, 01:45 PM
    Gauge 10 or 12 for 240 volts
    Installing a electric heater in my bathroom, the kind that go into the wall cavity between the studs. It requires 240 volts and 16-17 amps. What size wire and breaker are needed?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    May 31, 2007, 02:24 PM
    AWG gauge 12 wire can carry a max amp load of 41 and 10 gauge can carry a max of 55 amps. Both are heavier than you really need but if you already have both use the 12. TK will be hear later and can give you a specific on the breaker. I usually go up to the next breaker larger than the load, 20 amp.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    May 31, 2007, 02:40 PM
    Ballenger, can you cite a reference that lists the ampacities you offer?

    #12 wire when used in a builidng in the USA is max 20 amps, and #10 wire is 30 amps.

    These ampacities are all per the National Electric Code.

    Electric heat is to be considered as a 100 % continuous load. If the heater draws 16 amps, then #12 is fine, if the heater draws 17 amps, then #10 is needed.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    May 31, 2007, 03:26 PM
    Tom, go with TK. He is looking at my amp/gauge chart so I'm not sure of my answer on the gauge of wire. If you don't know how to pull 220 from your panel he will describe what's safe for a home owner to try. He says 10 gauge wire and he's the electrician.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Jun 4, 2007, 02:34 PM
    To get 240 volts from panel, you install a 2 pole 30 Amp breaker, You will get 240 volts from there. Every other breaker space, is the opposite phase(240)volts no matter where you install breaker.
    Like already been said, 3 #10's(2 hots and ground) 1 more #10 for neutral, if needed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do I get 240 volts AC to the hot tub? [ 9 Answers ]

Hello, everyone. My name is Mike and I live in Dunsford, Ontario, Canada. My wife recently purchased a new hot tub and has lovingly assigned the task of installing this monster to me... I have an older house with the old fashioned screw-in fuses, and 200 amp service. I had one spot remaining...

120 volts vs 240 volts tools [ 3 Answers ]

How do I configure a 120 volts 60hz woodworking tools bought in the usa to work on a 240 volts 50hz power rating in my country without having to compromise the motor operation. I understand that the stepdown transformer can only reduce the voltage but not the cycles. That means that a tool with...

2 wire 240 connect to 3 wire 120/240 [ 2 Answers ]

I am in the process of hooking up a new Electric Range. It has a three wire connector terminal block ). My existing wiring is 1970's vintage alum, but inspected and in good condition. The existing wire in 8 gauge two wire (black and white) plus ground. Do I have to run a new wire all the...

240 volt four wire in 240 three wire outlet [ 1 Answers ]

I have a generator that has (2) 20 amp 110 outlets and (1) 240 outlet. The 240 outlet have receptacle for four wire plug but I want to use it in a three 930 wire 240 volt plug at other end. Is this a workable solution?

Cl 200 220 volts ? [ 1 Answers ]

Does the CL 200 mean it's a 200 amp service? I can't see the numbers but I'm sure its 2-2-2 alu... the jacket is 1 inch wide 5/8 or so thick... what amp panel can I put in with that.. I have 100 amp service now.. I won't use more elect I just want a bigger box with 30 spaces for more room to...


View more questions Search