    Bryant 395CAV inside blower runs slow w/ AC start. What could cause this?
    Bryant 395CAV furnace. Capacitor outside replace a few years ago. Filter fine. When we kicked on the AC this year, the outside fan runs fine, the copper pipe in the house is cold, the thermostat kicks on the system, but the fan in the updraft blower runs slowly. Checked YouTube and pulled the motor housing to check the ohms (spelling?). Came in fine (fast wire was a lower number than each step down in speed). Fan turns easily using a finger. Fuse is good. Circuit board looks fine front and back. Capacitor on inside blower is not bulging. Cut power and no codes came up. Don't know how to check the relay.

    What else should should I be looking at to see why the fan runs slow? Many thanks for any help that can be given.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    May 30, 2015, 11:47 AM
    What was it doing that caused you to replace the capacitor?
    robmarx's Avatar
    robmarx Posts: 7, Reputation: 1
    New Member
     
    #3

    May 30, 2015, 12:12 PM
    It's been several years, but the outside compressor (was not the fan) just stopped running. Called a repair guy and after troubleshooting replaced the capacitor on the compressor and the AC system has been fine until the inside fan started with its problem yesterday.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #4

    May 30, 2015, 12:38 PM
    Check the voltage on the heat and cool speed on the control board.
    robmarx's Avatar
    robmarx Posts: 7, Reputation: 1
    New Member
     
    #5

    May 31, 2015, 10:22 AM
    Quote Originally Posted by bitters View Post
    Check the voltage on the heat and cool speed on the control board.
    Voltage came in at approx 120 for all except the high speed. That came in at approx 85 volts.

    Added - cut power, pulled slow wire, reintroduced power, and the fan ran didn't run (fast wire still connected). Did same for fast wire and the fan ran slow (slow wire still connected. Hope this helps with the diagnostic.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #6

    May 31, 2015, 10:59 AM
    Pull the wires off sec 1 and sec 2 and make sure you have 24V.
    robmarx's Avatar
    robmarx Posts: 7, Reputation: 1
    New Member
     
    #7

    May 31, 2015, 11:06 AM
    Quote Originally Posted by bitters View Post
    Pull the wires off sec 1 and sec 2 and make sure you have 24V.
    27 volts on each.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #8

    May 31, 2015, 12:35 PM
    OK 27v is a good reading. With the stat calling for cooling. Check the voltage on the cool connection and common. You should have 120V.
    robmarx's Avatar
    robmarx Posts: 7, Reputation: 1
    New Member
     
    #9

    May 31, 2015, 01:17 PM
    Quote Originally Posted by bitters View Post
    OK 27v is a good reading. With the stat calling for cooling. Check the voltage on the cool connection and common. You should have 120V.

    Cool (black hi speed) comes back with 120v.

    Another update. Running stat on cool, the fan kicks in on slow speed for 5-6 seconds then stops - like its expecting something else to kick in the higher speed. After about a minute the slow fan kicks in for a few seconds only to again stop. It does this a few times. I can feel the cold air as it radiates down from the coils. Feels like sitting in front of an open freezer (reaaaaaly nice given today's temperature).


    I have an infrared thermometer and the area around the hub of the motor is between 110 and 130 F.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #10

    May 31, 2015, 02:13 PM
    Try taking the Yellow wire off the "spare" terminal and pull the black wire off the cool terminal. Put the yellow wire on cool.
    robmarx's Avatar
    robmarx Posts: 7, Reputation: 1
    New Member
     
    #11

    May 31, 2015, 02:36 PM
    Quote Originally Posted by bitters View Post
    Try taking the Yellow wire off the "spare" terminal and pull the black wire off the cool terminal. Put the yellow wire on cool.
    It does the same thing as when the black wire was on - runs slow then stops then slow then stops.

    edit. I'm beginning to think its the motor. When the motor stops running (in between the session of running slow I described above) the end of the motor (not the hub, but the lattice structure around the hub) gets up to 155 F then cools off while the fan runs, then heats up, etc. like its getting power but instead of running just heats up. Bad smell, too. Like hot electrical. Lee in mind, I'm just an average Joe homeowner, not an HVAC guru, so I'm describing everything like an unskilled, unpaid helper would.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #12

    May 31, 2015, 02:51 PM
    Quote Originally Posted by robmarx View Post
    It does the same thing as when the black wire was on - runs slow then stops then slow then stops.
    Yea sounds like the motor is going bad.

    Let me know if you need help replacing it.
    robmarx's Avatar
    robmarx Posts: 7, Reputation: 1
    New Member
     
    #13

    May 31, 2015, 02:55 PM
    Quote Originally Posted by bitters View Post
    Yea sounds like the motor is going bad.

    Let me know if you need help replacing it.
    I reaaaaaaaly appreciate all your help. You, my friend, are a good person. Have a great rest of the weekend. I'll drop a note when I've swapped the motor out.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #14

    May 31, 2015, 03:39 PM
    Thanks for the kind words!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant Plus 90 blower runs intermittently [ 7 Answers ]

I have a Bryant 90 Plus (350 MAV) gas furnace that is about 13 years old with an intermittent problem. The inducer motor starts, igniter lights, gas valve opens, and burner lights and runs but occasionally the blower motor will not start. When this occurs the plenum attached to the furnace gets...

Bryant 3/4 hp blower start up problems... runs OK. [ 1 Answers ]

I have a bryant 3/4 hp blower running at 15.34 or so amps. Is that correct. The blower runs OK if I leave it running. If I turn it off, I need to spin the drum to get it to move again. Is this a problem with the capacitor or the motor? Any advice...

Snow Blower, runs when cold, then stops and runs slow & erratic [ 0 Answers ]

When frist started, it runs great. After a while using it, it start running rough. The only way I keep it running, is playing with the choke lever, and then it still can't be used. RPM are down, & runs rough. No power, & when I move the throttle down it runs even for a second, then back to rough,...

Bryant 395CAV blower speeds [ 1 Answers ]

Hello, It appears that my furnace (Bryant 395CAV) isn't blowing cool air at a high enough speed. I don't feel that the house is as cool as it should be - the air coming from the vents is cold, although it doesn't seem to circulate around as much as it could. I've done some "balancing" and...

Bryant 395CAV Furnace Won't Start [ 3 Answers ]

The furnace typically takes three or four ignition cycles before flame extends down burner to reach the flame sensor. It seems to light only halfway down burner on most attempts. Sometimes reaches shut off and then I have to flick switch to repeat cycle. Help.


View more questions Search