Heating Issue
I'm having a little trouble with my furnace. The furnace will not go on unless I move the thermostat to the on position. When I switch the thermostat back to auto the heater will shut off within a minute or two. I do not believe it cycles down... the furnace blows heat for that minute or two and then Shuts down. It may also be worth noting that air conditioner works as it should.
I have a Lennox electric furnace model CB26UH-030-R-230-1
|
|
|
Ultra Member
|
|
Jan 9, 2015, 03:30 PM
|
|
Remove the thermostat & connect the wires on the R & W terminals together. If the furnace then fires the problem is the stat.
|
|
|
New Member
|
|
Jan 9, 2015, 04:25 PM
|
|
Grady, thanks for tip. I tried that and it fired up once, but I could not duplicate it. A couple of times I heard the furnace try to kick in but it did not. I have never heard it do that. I think I will try changing the stat and take it from there.
|
|
|
Ultra Member
|
|
Jan 9, 2015, 06:51 PM
|
|
I don't know if your furnace has one or not but look for a blinking LED (usually red), count the blinks & look inside the blower compartment door for the key to the blink code.
|
|
|
Uber Member
|
|
Jan 9, 2015, 07:36 PM
|
|
With an electric furnace it could be the sequencer. Be careful working with the sequencer, some Lennox units have 240VAC sequencers.
|
|
|
New Member
|
|
Jan 10, 2015, 06:59 PM
|
|
So I changed out the stat and all seems to be working well for now. Thank you very much!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Heating Issue
[ 0 Answers ]
I have a Coleman furnace model no. DGAAO70BDTA. When I set the thermostat on Auto and Heat nothing happens. The AC works fine.
Heating issue
[ 1 Answers ]
My carrier furnace board led light blinks 3 times fast and 3 times slow what does it mean
Heating issue with Freedom 75
[ 2 Answers ]
Hello. I have an American Standard Freedom 75 gas furnace, and it's acting up a bit. The furnace will run fine when it is first turned on at the thermostat, and will heat the house properly, but once it cycles off, the next time it comes on, the blower will just continuously blow, but no heat...
Heating issue!
[ 19 Answers ]
I have a conventional heating and cooling unit for my condo. This is not a heat pump. The outside unit is a Rheem. The problem I am having is that when I turn on my heat, the settings are set to fan-auto, system-heat, I have no heat coming out of the vents just plain air. Now if I set the fan to...
View more questions
Search
|