    Heating Question
    I am working on an American Standard furnace that will not cycle off & on. It works only in the "On" position but the air conditioner cycles on & off fine. I have already replaced the thermostat.

    Can someone tell me what the problem may be?
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #2

    Sep 13, 2014, 02:50 PM
    What's model number of the furnace?
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #3

    Sep 20, 2014, 03:59 PM
    My model # is TWGO25A140B1
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #4

    Sep 21, 2014, 11:23 AM
    Take the stat off and move G wire to Y terminal, so you have two wires on Y and see what happens. Turn power off to furnace.

    I can't find anything on that model #.
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #5

    Sep 21, 2014, 02:07 PM
    Thanks for the response. I turned off power to furnace and moved G wire to Y terminal, turned power back on to furnace and tried to cycle it on. Nothing.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #6

    Sep 21, 2014, 03:57 PM
    Did the AC come on? But no fan?
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #7

    Sep 21, 2014, 06:29 PM
    Did not hear the AC kick on-definitely no fan. The AC cycles on and off normally. But the heat works only when on ON and not when on AUTO.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #8

    Sep 22, 2014, 06:16 AM
    Can you double check the model #? What brand is the furnace? The model number should be inside the top panel (burner compartment) of the furnace.
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #9

    Sep 22, 2014, 06:43 PM
    American Standard TWG025A140B1 I don't know if the 0's are O's or vise-versa.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #10

    Sep 23, 2014, 09:12 AM
    There is very limited info about your furnace on the net. Does the furnace have electric heat coils? If so it could have a bad sequencer. Can you post a close up pic of the wiring diagram?
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #11

    Sep 24, 2014, 04:36 PM
    Appreciate your help bitters! The furnace have electric heat coils. I hope you can read these diagrams. Attachment 46608 Attachment 46609
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #12

    Sep 25, 2014, 09:17 AM
    Quote Originally Posted by RJackson4016 View Post
    Appreciate your help bitters! The furnace have electric heat coils. I hope you can read these diagrams. Attachment 46608 Attachment 46609
    I can't open your attachments. Still would like to see them.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #13

    Sep 25, 2014, 09:21 AM
    Rjackson, this link will show you how to post a picture, I hope it helps. https://www.askmehelpdesk.com/suppor...es-783127.html
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #14

    Sep 25, 2014, 05:47 PM
    Thanks parttime! Try this bitters. (Attached below)
    Attached Images
      
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #15

    Sep 26, 2014, 09:08 AM
    Thanks for the drawings. I don't see see anything in there that would be causing the problem. If you have a voltmeter, set the stat to cool and fan to auto. Then go to the furnace and put your meter on B and T on the circuit board. Make sure the door switch is engaged. If you have 0 volts something is going on in the stat. If you have 24 volts then the circuit board has a problem.
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #16

    Sep 26, 2014, 05:36 PM
    Okay. I have a meter and will do that, but I have replaced the stat so it's fairly new.
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #17

    Oct 7, 2014, 05:45 PM
    Heating Problem
    Hi bitters. I realized the wire diagrams I sent to you earlier were the wrong ones. This diagram is from the "Heater Control Box" and maybe it might help you with my problem. Thanks again.
    Attached Images
     
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #18

    Oct 7, 2014, 06:19 PM
    The diagram is no where near complete. We need to be able to see the whole thing.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #19

    Oct 7, 2014, 06:45 PM
    Are you still working on the furnace problem where you said the heat would not come on when the switch on the thermostat was set to "ON"
    RJackson4016's Avatar
    RJackson4016 Posts: 54, Reputation: 1
    Junior Member
     
    #20

    Oct 9, 2014, 05:40 PM
    Yes-I'm thinking about searching for the relay or sequencer online as a process of elimination, hoping that will solve the problem.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant Heating Question [ 2 Answers ]

I can't keep the flames going on my Bryant furnace. I have two units, upstairs and downstairs. Upstairs is working fine. Downstairs- I followed the instructions to "relight", the coil got hot, the flames came on, but after a few seconds shut down. It makes two or three attempts, then shuts...

Question about my furnace not heating up [ 0 Answers ]

My furnace will not put out heat ,a number code came on 33 it has a new filter and a couple of the ducts had lose tape but as of yesterday the heat is not working I have 3 small kids and I keep my dad with me here and it is COLD, one time today as it was being reset it kicked on for a minute then...

Heating Question [ 1 Answers ]

How long does it take for the central heating to come one in the living room? Please reply. Its for an exam. Thank you

Heating Oil Question [ 4 Answers ]

Heating oil here is OUTRAGEOUS... over $3 a gallon for #2 fuel oil... can I run kerosene instead which is only $2.20 a gallon?if so what will the long term damage be to my furnace... im really really short on cash right now but I don't want to blow my furnace up or anything... I've already bought...


View more questions Search