Step down transformers
How many amps, at 400 volts, can I get from a 300 kva [ 480v/ 400v] transformer?
|
|
|
Full Member
|
|
Apr 8, 2007, 06:12 AM
|
|
Originally Posted by Nathonian
How many amps, at 400 volts, can I get from a 300 kva [ 480v/ 400v] transformer?
This answer can vary depending on the type of load. Assuming a non-inductive load,(no large motors) then your answer would be 300kva/400volts output=750 amps. This is in an ideal situation. In reality you have a less then perfect energy transfer, the "standard" for industrial applications is usually to caclulate for a 60% efficiency or Power Factor(PF). In this case 300kva*.6PF =180000/400volts yields you approximatley 450 Amps.
Hope This Helps,
Morrowrj
|
|
|
Uber Member
|
|
Apr 8, 2007, 08:12 AM
|
|
The expression Volt Amps of AC power, will include any power factor consideration on the circuit. A transformer rated in KVA will not need to be derated for any inductive or capacitive load.
Assuming this is a 3 phase transformer, due to the size and voltages involved, the amps available on the 400 volt secondary side is calculated:
300,000 VA / 400 volts * 1.73= 1297.5 or 1300 amps
|
|
|
Full Member
|
|
Apr 8, 2007, 04:30 PM
|
|
Hmm, I normally work single phase... However it still seems like your calculation is off? Is it possible that the equation is KVa divided by the quantity of volts times 1.73 ?
300,000VA / (400 V * 1.73)
or
300,000Va / 692 = 433 Amps.
Please see here : Rex Power Magnetics - Home Page
Or here : How To Size Phase Transformers
Please let me know if I am missing something.
Morrowrj
|
|
|
Uber Member
|
|
Apr 10, 2007, 01:26 AM
|
|
Sorry I missed this, thought I would get subscribed just by answering.
You are right ,I can't believe I said that. The brackets mean to calc phase to phase voltage of 692, then divide.
Morrow is correct, the amps is 433.
|
|
|
New Member
|
|
Jun 1, 2007, 05:52 PM
|
|
Hello There
|
|
|
New Member
|
|
Jun 1, 2007, 05:54 PM
|
|
Sorry New, What Would Be The Right Size Transformer.
Power Coming In Would Be Single Phase 480
Output Is 120v , About 4.2a
I Figure About 1kva Would Be Plenty
|
|
|
Full Member
|
|
Jun 3, 2007, 05:55 AM
|
|
Yes, I agree 1kva should be good. Did you check the links I referenced above?
Morrowrj
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Step by step needed to become and operate as a Talent Agent
[ 17 Answers ]
Hi,
I am interested in operating a Talent agency of my own, and would appreciate any information on where to begin the process. I know I need to get licensed and a surety bond in the amount of $50,000 according to the new standards, but I need to know where to go to get the application for...
What are the names of the different cartoons in the transformers series
[ 1 Answers ]
Ok the only thing I know is that there are The orignial 98 episodes, that's the old transformers, and then there's beast wars, headmaster, armada, cybertron, but what order are these in and what am I missing?? I am looking to download all of that onto a DVD/CD and watch it on my comp.
How to partition a hard drive step by step?
[ 2 Answers ]
Downloaded a program and it formatted my hard drive.
Have a 20 gig hard drive after it done this, it now reads 12 gig
Can anybody help get the 20 gig back
Need steps to clear this up, I don't know anything about hard drives. I'm running Xp Home on HP. Pavilion.
Help
Transformers/inverters?
[ 2 Answers ]
I need to replace some transformers to gadgets:
a) How do I find out which one to buy?
b) Where do I get them cheaply?
c) Is a generic (by spec only) as safe as the original?
Thanks
Help with transformers PLEASE!
[ 1 Answers ]
I have to make a simple transformer, that measures the output voltage from the secondary coil, with relation to the distance between the primary and the secondary coil. So, I don't have to make it a step up or step down transformer, I just have to see how the voltage changes with distance. So do...
View more questions
Search
|