    Help! We cant figure out how stray voltage is getting in our pool
    I put in a pool last summer and it is has given us a slight sting on fingers since the first week. We have called everyone and no one can tell us how the power is getting in the pool. How can you bond a pool to existing concrete? I think the pools bonding grid isn't correct or we would not feel the sting.
    They say power ould be coming in from the ground rod to the light to the pool... bonding should protect us against that.
    helpfast's Avatar
    helpfast Posts: 6, Reputation: 1
    New Member
     
    #2

    May 22, 2014, 10:58 AM
    Also: can anyone tell me where I can find an inspector to tell me if the pool is bonded or not?? I can't seem to get a straight answer on anything concerning this issue.
    smoothy's Avatar
    smoothy Posts: 25,492, Reputation: 2853
    Uber Member
     
    #3

    May 22, 2014, 11:03 AM
    Hire a licensed Electrician... explain the problem... they should be able to find and fix the problem. This is a very dangerous and serious matter.
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #4

    May 22, 2014, 12:41 PM
    Do you have pumps etc. circulating or cleaning the water in the pool? Are the pumps protected by GFCI breakers? Does the pool have a light? If you are getting shocked, there is definitely a potential difference and or leakage current. If you are standing on the concrete and touch the water and get shocked, they are definitely not at the same potential. If you are at a different potential, then your bonding is not good enough or non-existent.

    Newer concrete swimming pools are full of rebar that is bonded to the hilt to maintain equal potentials at all points in the pool. I have experienced in the past a situation where the swimming pool concrete was built before these codes were in place. The owner said that occasionally someone would say they were shocked by touching the surrounding wet cement outside the pool. The pool was fed by natural hot springs, so no pumps etc. were used. I eventually found a sump pump down stream from the pool that was dumping water into the same stream as the water exiting the pool had issues. The sump pump was not protected by a GFCI breaker and the water leading back to the pool was slightly energized when the sump pump kicked on. The concrete around the pool was new with rebar etc. embedded in it and not attached to rebar in the pool if there even is any in a pool this old. The swimming pool had to be at a higher resistance to ground than the newer concrete around it, thus allowing the pool to be at a different potential than the concrete around it. The issue was resolved by replacing the sump pump with a different type and installing a GFCI breaker on the sump pump. The bonding issue will never be fixed until they replace the cement pool and bond its rebar etc. to the rebar of the surrounding concrete. In one training session I had with the engineers from the power company, they explained that it was possible for a person to be swimming in the water not touching anything but the water and the potential between their head and feet could under rare circumstances be enough different to electrocute them. A little far fetched, but bonding and grounding of swimming pools and proper grounding, bonding and GFCI protection of electrical equipment are really critical in a swimming pool. Not something to ignore!
    helpfast's Avatar
    helpfast Posts: 6, Reputation: 1
    New Member
     
    #5

    May 23, 2014, 07:48 AM
    I have hired an electrician. And had the local utlities company came out as well. No one can tell me how the stray is getting in the pool. The entire power is off on the street and it is still there. They think it is backfeeding through my ground rod and getting in through the light. How can we bond the pool to the concrete without ripping out all the concrete? The sting is only felt on a tiny cut if you are touching wet concrete and pool water. The pool is saltwater. Would more grounding rods help?It is so sad to just recently pay so much for a pool and not be able to use it.
    helpfast's Avatar
    helpfast Posts: 6, Reputation: 1
    New Member
     
    #6

    May 23, 2014, 07:50 AM
    Yes we have pumps, heater, saltwater generator, light, slide, diving board. 16 by 32 inground liner.
    GFCI protection as well (shouldnt that trip if it got high enough to be electrocuted) the breakers I think are giving me a false sense of protection.
    helpfast's Avatar
    helpfast Posts: 6, Reputation: 1
    New Member
     
    #7

    May 23, 2014, 08:00 AM
    This is so stressful and to have spent so much money on a pool and not be able to use it. No one can seem to help us within our reach. Probably the best thing to do would be to fill it in and to think it was only a year ago we were sooooo excited about our new pool
    smoothy's Avatar
    smoothy Posts: 25,492, Reputation: 2853
    Uber Member
     
    #8

    May 23, 2014, 09:16 AM
    Maybe find another electrician first... like every other field, they all aren't equally talented.
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #9

    May 23, 2014, 11:50 AM
    I get accused of lengthy answers, but this will be my last. The power company is probably at fault, but unwilling to do what it takes to find it. I had a similar situation a few years ago. I did the necessary assessment and told the home owner they needed to contact the power company because the issue was on their side. They did, the power company spent 3 days checking and finally found the issue on a capacitor bank 2 blocks away from their home. That's all I am going to say.
    helpfast's Avatar
    helpfast Posts: 6, Reputation: 1
    New Member
     
    #10

    May 23, 2014, 12:06 PM
    In your opinion do you think a pool can be correctly bonded and have electricity bleed into the pool backfeeding from the ground rod?
    I don't want to tear up concrete and find the pool corectly bonded... :(
    And we apprecitate your lengthy answers! WE NEED Help.
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #11

    May 23, 2014, 12:09 PM
    I have to get into a theory discussion, and I don't want to offend those who like short answers, If you want to address me privately I will try explain what is going on. And thank you.
    Cat1864's Avatar
    Cat1864 Posts: 8,007, Reputation: 3687
    Marriage Expert
     
    #12

    May 23, 2014, 12:50 PM
    Quote Originally Posted by Studs ad View Post
    I have to get into a theory discussion, and I don't want to offend those who like short answers, If you want to address me privately I will try explain what is going on. And thank you.
    Please keep all advice on the board.

    Thank you.


    I have no experience in this subject but would love to read what you think might be happening. It may also help other come up with ideas on what the issue could be.
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #13

    May 23, 2014, 11:23 PM
    I spent the last 8 hours trying to explain how to test and evaluate how to troubleshoot your system. I finally got it worked down to a few simple tests. I wrote up the procedure and the thought process and sent it. I checked your responses and it never showed up. It is past midnight here and I started at about 1 this afternoon. I am not going to re-write it again tonight. There are answers and they will take some time to test out. You will need the assistance of an electrician probably. I am almost positive that there is a fault somewhere that is causing your issue and that the fault originates outside of the area that the power company shut off. To put your mind at ease a little, the problem wasn't there when they installed the pool. Bonding or no bonding the problem appears to have been created since installation. Better bonding may have masked the fault, but it would still be there okay. So assume something changed since installation. Assume that it is outside the boundaries that you turned the power off to. That leaves basically to directions- one is that the fault current is coming in from your water supply. It means that a few things have to be just right, but I know how to test for it. The other is that it is coming through the earth itself and I know how to test for that. I will contact you further at your request. I am not exploring your power system at this time because my evaluation tells me that it most likely didn't come that direction. If the other two directions lead to a dead end we will go down this road later. Thanks for trusting me a little. I get a little frustrated sometimes. Respect is always earned. Friendship I appreciate. A challenge I enjoy. You have given me an opportunity for all the above.
    Thank you!
    Studs ad's Avatar
    Studs ad Posts: 134, Reputation: 9
    Junior Member
     
    #14

    May 27, 2014, 09:47 PM
    Quote Originally Posted by Studs ad View Post
    I spent the last 8 hours trying to explain how to test and evaluate how to troubleshoot your system. I finally got it worked down to a few simple tests. I wrote up the procedure and the thought process and sent it. I checked your responses and it never showed up. It is past midnight here and I started at about 1 this afternoon. I am not going to re-write it again tonight. There are answers and they will take some time to test out. You will need the assistance of an electrician probably. I am almost positive that there is a fault somewhere that is causing your issue and that the fault originates outside of the area that the power company shut off. To put your mind at ease a little, the problem wasn't there when they installed the pool. Bonding or no bonding the problem appears to have been created since installation. Better bonding may have masked the fault, but it would still be there okay. So assume something changed since installation. Assume that it is outside the boundaries that you turned the power off to. That leaves basically to directions- one is that the fault current is coming in from your water supply. It means that a few things have to be just right, but I know how to test for it. The other is that it is coming through the earth itself and I know how to test for that. I will contact you further at your request. I am not exploring your power system at this time because my evaluation tells me that it most likely didn't come that direction. If the other two directions lead to a dead end we will go down this road later. Thanks for trusting me a little. I get a little frustrated sometimes. Respect is always earned. Friendship I appreciate. A challenge I enjoy. You have given me an opportunity for all the above.
    Thank you!
    Are you ready to try something?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

CHALLENGING QUESTION: Low-voltage switch in a high-voltage circuit? [ 6 Answers ]

A project I'm working on has an air pump and a water pump that run during operation. When the water tank that the water pump draws from becomes empty, a liquid level switch will be used to shut off both pumps. The original plan was to just place the switch in series with the power supply for...

How do you figure three phase amps when all you know is voltage and wattage. [ 1 Answers ]

How do you figure three phase amps. When all you know is the voltage and the wattage. Do not know the PF factor

Halogen - line voltage (120v) or low voltage (12v) [ 5 Answers ]

Hi. I am renovating the kitchen and plan to install small halogen MR16 ceiling pot lights. Contrast and Lightolier have been recommended. At least, the Contrast line is available with either line or low voltage feeds. These questions come up as the plan calls for 9x35w MR16 (ceiling pot...

Track lights: low voltage vs line voltage.comsume the same electricity in the end? [ 11 Answers ]

Hi! I just installed a section of track light in my living room just to see what it would look like and so far I'm not convinced... you see, I had a regular celing lamp with a 75w incandescent bulb and the room was very well lit... now with the track light I find that I need 3 fixtures with halogen...

220 Voltage how do I figure the amp 100 or 200? [ 3 Answers ]

Hi I am a realtor and I have a buyer that wants to know what the amps are in a residential home. The voltage is 220 but I can't figure out the amps. This is a transaction that I am currently working on and it sounds like the amps is the deal breaker. Help! Anna


View more questions Search