    Plumbing Vent Issue
    My main stack/vent which penetrates my roof is 4" plastic. It comes down vertical until it gets to the first floor ceiling where is turns 90 deg and runs horizontal to an outside wall. About 3 feet from this 90 deg elbow there is a "Y" connection for a toilet. I'm not sure but I assume at the point of the toilet connection this main stack stops being a vent and starts being a drain. I have a 2" vent from floors below which I would like to connect to the main vent or stack. Can I connect this pipe to the horizontal 4" pipe between the toilet and the 90 deg elbow or do I need to connect to the stack on the other side of the 90 deg elbow where it is vertical?
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #2

    Apr 1, 2007, 12:10 AM
    Quote Originally Posted by GWeb
    My main stack/vent which penetrates my roof is 4" plastic. It comes down vertical until it gets to the first floor ceiling where is turns 90 deg and runs horizontal to an outside wall. About 3 feet from this 90 deg elbow there is a "Y" connection for a toilet. I'm not sure but I assume at the point of the toilet connection this main stack stops being a vent and starts being a drain. I have a 2" vent from floors below which I would like to connect to the main vent or stack. Can I connect this pipe to the horizontal 4" pipe between the toilet and the 90 deg elbow or do I need to connect to the stack on the other side of the 90 deg elbow where it is vertical?
    You need to be at least six inches above the flood rim of the water closet before you can combine your 2" vent into the existing vent.

    The flood rim is the top of the water closet bowl, by the way.
    GWeb's Avatar
    GWeb Posts: 3, Reputation: 1
    New Member
     
    #3

    Apr 1, 2007, 05:23 AM
    Combining Vents?
    Is there any reason why two 2" vent pipes can't be combined? I have a 2" vent from my basement and I need another 2" vent at the main floor for my kitchen. I would like to combine the two into one which will then continue on to connect to the main 4" vent to the house located above.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Apr 1, 2007, 05:26 AM
    Web,

    You are correct when you say, "I'm not sure but I assume at the point of the toilet connection this main stack stops being a vent and starts being a drain."
    It stops being a vent stack and starts being a stack vent.
    And growler's correct with his advice. What you're planning is called a "revent" and a revent MUST be connected at least 6 inches above
    The flood rim of the highest fixture.

    As for combining two 2" vents it all boils down to how many fixture units will be on the vent. Code allows 20 fixture units on a 2" vent. If your basement group consists of a toilet, lavatory, shower, and a washer that would give you nine fixture units. Add a kitchen with a disposal and you have another three units. They add up to 12 fixture units so merge the two vents. Just remenber growlers advice and revent back 6" above the rim of the toilet. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why are there vents? [ 1 Answers ]

:confused: Okay, it looks like moving the toilet is way beyond my diy skills right now. So I am back to the original plan of just moving the supply lines. Ripping the drywall off has revealed even more interesting things. The cold water pipe looks like that mousetrap game with more turns than a...

Sewer Vents [ 1 Answers ]

I have a new home on a conventinal septic system/leach filed with a grinder pump. I have noticed sewer smells in the basement in the past and now the smell has moved to under the kitchen sink, and I do see a vent pipe here. We have rough plumbing in the basement for an future bathroom/shower. There...

Combining Nitrix Oxide With Caffenine [ 1 Answers ]

I Am Taking Nitrix Oxide & I Know Caffenine Should Not Be Combined With It. I Want To Know If It Would Interfere If I Had Caffenine Only Once A Week.

Combining Sink Drains [ 2 Answers ]

Hi, I'm putting in a makeshift kitchenette on the first floor of my house. The sink is going in a closet that shares a wall with the bathroom. The water lines are already there, so that's no problem. However, There is no drain. I'm wondering if I can combine the drain to the kitchen sink...


View more questions Search