    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #1

    Dec 4, 2013, 10:11 AM
    Starting up furnace
    Hello! It's getting colder with every day, so I somehow have to fix our furnace. It's an older model that came with the house (please refer to attached photos), which worked fine when we tested a few months ago. Looked like the pilot had stayed lit for years and years before I shut down the gas main to install gas dryer. The furnace pilot went out and I can't light it back on, unlike the gas water heater pilot.

    I would like to find a troubleshooting manual/procedure to see what's failing and if this is something I can work on myself. I have contacted the manufacturer with emails and phone messages -- to no avail: no response whatsoever.

    It's also good to know what's wrong before hiring a HVAC person.

    What I have tested: the fuse is good; the power is supplied; the mercury switch is sparkling when switched; I smell gas when trying to light the pilot.

    Any suggestion would be greatly appreciated!
    Attached Images
       
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Dec 4, 2013, 11:37 AM
    Does this furnace have a standing pilot light or an electronic igniter?
    Are those the lighting instructions behind the gas valve
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #3

    Dec 4, 2013, 12:18 PM
    Quote Originally Posted by hkstroud View Post
    Does this furnace have a standing pilot light or an electronic igniter?
    Are those the lighting instructions behind the gas valve
    Yes, you are right, those are the instructions. Looks like a standing pilot light to me, the one you have to light with a match -- isn't this what the instructions say?

    Looks like the pilot is dirty or out of adjustment, even though nothing has been done to it since its working times.
    Attached Images
     
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #4

    Dec 4, 2013, 01:05 PM
    Well, thanks for the feedback. I have tried repeatedly and the pilot is finally lit and stays up. Removing one of the covers to bring a burning match right next to the pilot opening helped.

    The only thing that worries me is that the pilot flame is pretty strong: it well overshoots the thermocouple and heats the metal surface behind to a red hot (as in the image attached). Is there a way to turn the pilot down a bit?
    Attached Images
     
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Dec 4, 2013, 01:27 PM
    On some of the older valves, there is a pilot adjustment screw. In some cases you can tighten down the screw. In others, you remove the cover screw and the adjustment is underneath. I believe the screw in the picture is the hold down screw for the thermocouple assembly. The new heaters of course save money by not having a pilot.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #6

    Dec 4, 2013, 02:09 PM
    I agree with Brian, there should be an adjustment on the gas valve for the pilot light. Keep in mind though that the pilot not only heats the thermocouple, it lights the burner.
    DennisMooreAC's Avatar
    DennisMooreAC Posts: 5, Reputation: 1
    New Member
     
    #7

    Dec 4, 2013, 04:12 PM
    I suggest doing a carbon monoxide check.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #8

    Dec 4, 2013, 05:51 PM
    Quote Originally Posted by DennisMooreAC View Post
    I suggest doing a carbon monoxide check.
    Thanks, a good point, totally forgot about it. The furnace itself is in a garage with a lower level of the floor. Do you mean checking the air pumped in the rooms for CO?
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #9

    Dec 4, 2013, 05:58 PM
    Quote Originally Posted by ma0641 View Post
    On some of the older valves, there is a pilot adjustment screw. In some cases you can tighten down the screw. In others, you remove the cover screw and the adjustment is underneath. I believe the screw in the picture is the hold down screw for the thermocouple assembly. The new heaters of course save money by not having a pilot.
    Thanks Brian and Harold! This is what the pilot gas line has. The photos show the flame end and the other end, with just a bare line free of screws or anything in between. Can't find anything like an adjustment screw, not much to tweak here at all.

    Could it be the screw on the right in the second photo?
    Attached Images
      
    DennisMooreAC's Avatar
    DennisMooreAC Posts: 5, Reputation: 1
    New Member
     
    #10

    Dec 4, 2013, 05:59 PM
    Check any areas with human habitation. 33 parts per million carbon monoxide starts making people sick.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #11

    Dec 4, 2013, 06:05 PM
    Quote Originally Posted by DennisMooreAC View Post
    Check any areas with human habitation. 33 parts per million carbon monoxide starts making people sick.
    Would a store bought CO senson/alarm be sufficient?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #12

    Dec 4, 2013, 07:22 PM
    Don't think so. Hard to tell. If you Google the gas valve model #, it may show you a schematic. I would also see if the little red plastic cap ( if it is a cap)comes off, it may be under there although it looks like an index mark. One thing I would do is to shut things down and vac out all the dust and rust. Use a small vac and a paint brush. Pilot doesn't seem too big. First indication of CO is a headache.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #13

    Dec 12, 2013, 10:25 AM
    Follow the pilot gas line back to the gas valve. Adjustment would be on the gas valve and should be close to the pilot gas line. Adjustment may be a recessed hex screw.

    Carbon monoxide detectors in all sleeping areas is a good idea.
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #14

    Dec 12, 2013, 10:59 AM
    Quote Originally Posted by hkstroud View Post
    Follow the pilot gas line back to the gas valve. Adjustment would be on the gas valve and should be close to the pilot gas line. Adjustment may be a recessed hex screw.

    Carbon monoxide detectors in all sleeping areas is a good idea.
    Thanks! No, nothing around the pilot line that could be tweaked. Must be a really old model.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #15

    Dec 12, 2013, 04:47 PM
    I certainly would expect there would be some means of adjusting the flame of the pilot.
    Can you find make and model of gas valve?
    Attached Images
     
    harum's Avatar
    harum Posts: 339, Reputation: 27
    Full Member
     
    #16

    Dec 13, 2013, 01:39 PM
    Quote Originally Posted by hkstroud View Post
    I certainly would expect there would be some means of adjusting the flame of the pilot.
    Can you find make and model of gas valve?
    Thank you. The valve model V8243A1084-1 by "Honeywell". Looks like I have to take the cover off. Nice image!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Echelon 9.c furnace not starting [ 0 Answers ]

Hi everyone, have an echelon 9.c unit that tries to turn the furnace on and then gives me two red blinking lights as an error. Per the manual it's "pressure switch closed with inducer pressure below pressure switch setpoint. Check pressure switch." Any guidance as to how to fix this?

Furnace starting intermittently [ 0 Answers ]

I have a Bryant Plus-80 down draft natural gas furnace. It seems like it is not starting reliably. If I pull the power plug, it will start up when I plug it back in and run normally. However, a few hours later, it is flashing warning or error codes and not running. The error codes I have seen...

Furnace loud when starting [ 1 Answers ]

My furnace, when the motor first turns on, makes a really loud vibrating noise. It seems like the blowers start, the noise lessens in volume. It has been loud for a number of weeks, and finally yesterday I went downstairs to see if anything was loose, but didn't see anything. Any thought from...

Furnace not starting up.. [ 2 Answers ]

Hi, I am trying to figure out what is wrong with my Amana furnace. It does not turn on, I have checked (and changed) the switch on the furnace, and reset the circuit breaker on the main panel. I am wondering if the thermostat could be the problem or is it bigger than that? I ran the fan once or...

Furnace not starting up [ 1 Answers ]

Gentlemen, I have a Bryant high efficiency furnace approx. 16 years old so it is not the type with outside air intake, just your standard simple furnace. My problem is the furnace will decide it doesn't want to turn on. The house cools down, then I go and turn off then back on the on/off switch...


View more questions Search