Garage ceiling lights blowing out
As soon as I turn a new bulb into the socket in my garage ceiling the bulb blows out.
My power in the house is OK and at load center in the garage. I have 3 breakers for the ceiling lights and the wall outlets. The two outside breakers show no power but the center breaker on a Sperry SP-152A shows the ACV DB at 22. All the wires are tight too.
What's happening?
Thanks
Mike
|
|
|
Full Member
|
|
Sep 23, 2013, 02:04 PM
|
|
What country are you in?
What range is the meter in? Set it for ACV - 250. You don't read the DB line, that isn't the scale for volts. If you see where it says, just above the ACV arc, 10/50/250 one above the other, that's the scale to use.
What model panel do you have?
|
|
|
New Member
|
|
Sep 23, 2013, 03:08 PM
|
|
I'm set at V~250. When I check the hot and ground on the breaker it goes all the way to ACV 10,50,250.
Mike
|
|
|
New Member
|
|
Sep 23, 2013, 03:10 PM
|
|
I'm in the United States
Sorry
Mike
|
|
|
Uber Member
|
|
Sep 23, 2013, 03:26 PM
|
|
Sounds like you have somehow got a 2 hot wire setup and 240VAC. Sure 2 of the breakers aren't paired?
|
|
|
New Member
|
|
Sep 23, 2013, 03:44 PM
|
|
The 3 breakers are wired separately.
There is a 220v in the box also
And this entire problem could have happened during a storm. I just did not go into the garage for a couple of days after the storm.
Mike
|
|
|
New Member
|
|
Sep 23, 2013, 03:49 PM
|
|
My Load Center cover says:
Square D
120/240V. A.C. 1PH 3W.
Mains 100 AMP. MAX.
|
|
|
Full Member
|
|
Sep 23, 2013, 03:50 PM
|
|
Is there any way you can post a picture of the box?
You should have 3 or 4 heavy gauge wires coming into the panel. Hopefully you'll find one marked with white for the neutral and the ground should be green. The other two wires are the feed, if this is a 240 volt panel which it seems to be. Can you carefully measure from each of the hot wires to ground? If there are 4 wires can you also measure to neutral?
You may have lost a neutral.
|
|
|
New Member
|
|
Sep 23, 2013, 04:07 PM
|
|
There is a 3 wire power coming into the load center, two black and a bare ground.
|
|
|
New Member
|
|
Sep 23, 2013, 04:14 PM
|
|
I measured both the blacks they are showing 4,20,100 just at 110
|
|
|
New Member
|
|
Sep 23, 2013, 04:25 PM
|
|
If my power coming in is OK, and the 220 for the compressor is OK, could there be something wrong with the 3 breakers or the something inside the load center past the 220 breaker be bad, because the 220 breaker is first in the line?
Mike
|
|
|
Full Member
|
|
Sep 23, 2013, 04:40 PM
|
|
How many volts do you read at the light socket?
|
|
|
New Member
|
|
Sep 23, 2013, 05:12 PM
|
|
Acv 10/50/250
Same as the breaker
|
|
|
Uber Member
|
|
Sep 23, 2013, 05:16 PM
|
|
Originally Posted by mikeguyon
Acv 10/50/250
same as the breaker
What is 10/50/250? Sounds like a range, not a voltage.
|
|
|
New Member
|
|
Sep 23, 2013, 05:45 PM
|
|
I'm using a Sperry SP-152A analog meter. The ACV is recording all they way to the right. The only numbers showing are 10/50/250
|
|
|
Home Improvement & Construction Expert
|
|
Sep 23, 2013, 05:45 PM
|
|
Please review Sperry SP-152A instructions.
"To read AC voltage use the red “AC” arc. Use the
Numbers whose full scale reading matches the range
Selected by the “selector switch”."
Depending on voltage selector setting that is either 10 volts or 50 volts or 250 volts but we don't know which. Probably 250 since you are blowing bulbs.
Is this some thing new? What changes to wiring have been done? This is not something that "just happens"
|
|
|
New Member
|
|
Sep 23, 2013, 05:52 PM
|
|
Never had to do any repairs to the wiring. But we did have a bad storm go through. I'm set at V~250, it's reading 250
|
|
|
Home Improvement & Construction Expert
|
|
Sep 23, 2013, 05:54 PM
|
|
Set your selector above the highest possible voltage you could have. Since it is possible to have 240V, set selector to 250 or 1000, read actual voltage on scale that ends with the number 250.
|
|
|
Home Improvement & Construction Expert
|
|
Sep 23, 2013, 05:55 PM
|
|
And you are getting 250v at bulb holder?
|
|
|
New Member
|
|
Sep 23, 2013, 05:56 PM
|
|
Yes
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Changing lights in garage
[ 1 Answers ]
From the ceiling only 3 wires -- white, black, and bare ground
From the new fluorescent light ballast white, black, bare and red
What to do with the red?
5 lights in my garage
[ 3 Answers ]
I have 5 lights in my garage, I just changed two of the lights bulbs that were blown and replaced them with two new bulbs. Now the lights are dim and after about 5 seconds it is triggering the circuit breaker and killing all power to the garage and restroom on that circuit. It seems power is...
Exterior garage lights
[ 1 Answers ]
"Hello,
I want to have 2 exterior garage lights controlled by the garage door opener(GDO)so that the exterior lights come on when the GDO light comes on. But, I would also want the same 2 exterior lights controlled by a wall switch independently from the GDO.
Thanks"
Wondering why my lights keep blowing out
[ 2 Answers ]
I have been fighting with my husband because he said that their isn't a reason why my light bulbs keep blowing out. Meanwhile the dining room, living room and den which isn't on the same line keep blowing out. My worries is if this could cause any fires. Please give me some suggestions that I...