    Garage ceiling lights blowing out
    As soon as I turn a new bulb into the socket in my garage ceiling the bulb blows out.
    My power in the house is OK and at load center in the garage. I have 3 breakers for the ceiling lights and the wall outlets. The two outside breakers show no power but the center breaker on a Sperry SP-152A shows the ACV DB at 22. All the wires are tight too.

    What's happening?

    Thanks
    Mike
    medic-dan's Avatar
    medic-dan Posts: 321, Reputation: 23
    Full Member
     
    #2

    Sep 23, 2013, 02:04 PM
    What country are you in?

    What range is the meter in? Set it for ACV - 250. You don't read the DB line, that isn't the scale for volts. If you see where it says, just above the ACV arc, 10/50/250 one above the other, that's the scale to use.

    What model panel do you have?
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #3

    Sep 23, 2013, 03:08 PM
    I'm set at V~250. When I check the hot and ground on the breaker it goes all the way to ACV 10,50,250.

    Mike
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #4

    Sep 23, 2013, 03:10 PM
    I'm in the United States

    Sorry
    Mike
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Sep 23, 2013, 03:26 PM
    Sounds like you have somehow got a 2 hot wire setup and 240VAC. Sure 2 of the breakers aren't paired?
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #6

    Sep 23, 2013, 03:44 PM
    The 3 breakers are wired separately.

    There is a 220v in the box also

    And this entire problem could have happened during a storm. I just did not go into the garage for a couple of days after the storm.

    Mike
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #7

    Sep 23, 2013, 03:49 PM
    My Load Center cover says:

    Square D
    120/240V. A.C. 1PH 3W.
    Mains 100 AMP. MAX.
    medic-dan's Avatar
    medic-dan Posts: 321, Reputation: 23
    Full Member
     
    #8

    Sep 23, 2013, 03:50 PM
    Is there any way you can post a picture of the box?

    You should have 3 or 4 heavy gauge wires coming into the panel. Hopefully you'll find one marked with white for the neutral and the ground should be green. The other two wires are the feed, if this is a 240 volt panel which it seems to be. Can you carefully measure from each of the hot wires to ground? If there are 4 wires can you also measure to neutral?

    You may have lost a neutral.
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #9

    Sep 23, 2013, 04:07 PM
    There is a 3 wire power coming into the load center, two black and a bare ground.
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #10

    Sep 23, 2013, 04:14 PM
    I measured both the blacks they are showing 4,20,100 just at 110
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #11

    Sep 23, 2013, 04:25 PM
    If my power coming in is OK, and the 220 for the compressor is OK, could there be something wrong with the 3 breakers or the something inside the load center past the 220 breaker be bad, because the 220 breaker is first in the line?

    Mike
    medic-dan's Avatar
    medic-dan Posts: 321, Reputation: 23
    Full Member
     
    #12

    Sep 23, 2013, 04:40 PM
    How many volts do you read at the light socket?
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #13

    Sep 23, 2013, 05:12 PM
    Acv 10/50/250

    Same as the breaker
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #14

    Sep 23, 2013, 05:16 PM
    Quote Originally Posted by mikeguyon View Post
    Acv 10/50/250

    same as the breaker
    What is 10/50/250? Sounds like a range, not a voltage.
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #15

    Sep 23, 2013, 05:45 PM
    I'm using a Sperry SP-152A analog meter. The ACV is recording all they way to the right. The only numbers showing are 10/50/250
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #16

    Sep 23, 2013, 05:45 PM
    Please review Sperry SP-152A instructions.

    "To read AC voltage use the red “AC” arc. Use the
    Numbers whose full scale reading matches the range
    Selected by the “selector switch”."

    Depending on voltage selector setting that is either 10 volts or 50 volts or 250 volts but we don't know which. Probably 250 since you are blowing bulbs.

    Is this some thing new? What changes to wiring have been done? This is not something that "just happens"
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #17

    Sep 23, 2013, 05:52 PM
    Never had to do any repairs to the wiring. But we did have a bad storm go through. I'm set at V~250, it's reading 250
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #18

    Sep 23, 2013, 05:54 PM
    Set your selector above the highest possible voltage you could have. Since it is possible to have 240V, set selector to 250 or 1000, read actual voltage on scale that ends with the number 250.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #19

    Sep 23, 2013, 05:55 PM
    And you are getting 250v at bulb holder?
    mikeguyon's Avatar
    mikeguyon Posts: 14, Reputation: 1
    New Member
     
    #20

    Sep 23, 2013, 05:56 PM
    Yes

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Changing lights in garage [ 1 Answers ]

From the ceiling only 3 wires -- white, black, and bare ground From the new fluorescent light ballast white, black, bare and red What to do with the red?

Why is my ceiling fan lights blinking, when I turn on my lights. [ 2 Answers ]

My ceiling fan lights blink when I turn on my ceiling fan light... It does this when the fan is on or off... I have fluorescent lights the energy kind in my ceiling fan. My fans are 2 yrs old... And they are Harbor Breeze kind..

5 lights in my garage [ 3 Answers ]

I have 5 lights in my garage, I just changed two of the lights bulbs that were blown and replaced them with two new bulbs. Now the lights are dim and after about 5 seconds it is triggering the circuit breaker and killing all power to the garage and restroom on that circuit. It seems power is...