    Criterion Gas Furnace Draft Inducer Motor runs continuously.
    The draft inducer motor runs continuously. Thermostat set to off, inducer still runs. Heat and AC functions still operate normally but system never "shuts-down" after heat turns off. (Inducer motor runs during AC operation as well.) I suspect either the pressure switch or inducer motor relay are not releasing as they should. I saw a reference to condensate as a possible cause but not sure if there is any real connection there (You Tube video on inducer motors made quick comment that condensate could cause problem? ). Suggestions welcome...
    PJmax's Avatar
    PJmax Posts: 70, Reputation: 3
    Junior Member
     
    #2

    Nov 22, 2012, 07:01 PM
    It's not the pressure switch. It probably is the inducer fan relay.

    Pretty strange though... the control board should see that since the inducer is running that the draft proving (pressure) switch is showing closed before it should be. This is done on purpose so that you can not defeat or bypass a pressure switch issue.

    The long and short of the problem here is that you are probably going to need a new control module. I don't think the inducer relay is replaceable by itself.

    With a make and model number we could probably go further.
    Bobinorlfl's Avatar
    Bobinorlfl Posts: 4, Reputation: 1
    New Member
     
    #3

    Nov 22, 2012, 09:14 PM
    I suspect that you are right I just wanted to research a bit further to before buying a new IFC. It is Model # 1012-925A PN 62-24268-01 and is in a RGDJ-07EAUER Rheem Criterion Furnace. It seems that the Inducer Motor relay is probably hung-up in the always "on" position. I appreciate your input about not being able to replace the relay by itself -- I was considering that as a possible next move. I wish I had the schematic for the IDR instead of just a wiring diagram! Thanks...
    PJmax's Avatar
    PJmax Posts: 70, Reputation: 3
    Junior Member
     
    #4

    Nov 22, 2012, 10:15 PM
    I'll check out your model number later. If you are electronically inclined you could change the relay itself. It's going to be soldered to a p.c. board. You would have to match the relay based on sight as the company will not support any info like that.
    PJmax's Avatar
    PJmax Posts: 70, Reputation: 3
    Junior Member
     
    #5

    Nov 22, 2012, 10:24 PM
    This should be your board. Several relays on board. While I was looking at the board I came to think that it could also be a logic problem on the board. The board turns on the relay. The relay could actually be OK. A meter would be needed to check for relay status.
    Attached Images
     
    Bobinorlfl's Avatar
    Bobinorlfl Posts: 4, Reputation: 1
    New Member
     
    #6

    Nov 23, 2012, 06:55 AM
    Quote Originally Posted by PJmax View Post
    This should be your board. Several relays on board. While I was looking at the board I came to think that it could also be a logic problem on the board. The board turns on the relay. The relay could actually be ok. A meter would be needed to check for relay status.
    What type of logic problem do you think I might be encountering? My board is slightly different that the one you showed. I probably will have to study the circuit board and draw my own schematic of the exact relay so I can troubleshoot it.
    Attached Images
     
    PJmax's Avatar
    PJmax Posts: 70, Reputation: 3
    Junior Member
     
    #7

    Nov 23, 2012, 09:19 AM
    Trace out the foils from the inducer motor connection to the relay. One will most likely be a common neutral and the other should go to one contact on the relay. After you locate the correct relay on the board you'll need to use a meter to see if it's stuck closed. If the relay checks as normal then you may have a logic problem and there is no way to fix that. The logic is programmed on a chip and can't be read or altered any more.
    Bobinorlfl's Avatar
    Bobinorlfl Posts: 4, Reputation: 1
    New Member
     
    #8

    Nov 23, 2012, 10:38 AM
    Thanks for all your help! I'll post my findings after I am able to pull the board and do some more troubleshooting. I do appreciate your assistance!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Nordyne G7 furnace inducer & blower motor runs but furnace does not lite runs [ 0 Answers ]

Furnace inducer & blower motor operates but the furnace does not lite or burn

Rheem Criterion 2 draft inducer blower not running [ 0 Answers ]

Hello, I am having trouble with the Rheem Criterion 2 draft inducer blower not running. I have 2 green lights on the display. Can anyone help?

Draft inducer motor for Criterion II [ 2 Answers ]

What does the draft inducer motor do?

Draft inducer motor replaced on ruud furnace [ 0 Answers ]

I replaced a draft motor on my ruud 80% gas furnace,everything works except I noticed that it ignites almost immediately,say 2-3 seconds after draft motor starts as before it was about 10 seconds,does this matter?. it has standing pilot... the new motor didn't have the small holes at bottom of...

How do I find a source for replacement furnace draft inducer for rheem criterion II [ 2 Answers ]

I have A Rheem Criterion II Model RGLH-10EBRJR and I've been told I need to replace the draft inducer because of hairline cracks in the plastic housing. I looked at Rheem web site and no help there. How/where can I find a replacement part? Estimate from repairman was in excess of $400 for part...


View more questions Search