    RHEEM Gas Pack Self Contained Heat/AC-- The Blower shuts off after a couple minutes
    I have a rheem self contained gas pack LP heat & AC, I had a tech come look at it this past fall due to heat stop working, well he didn't help much to say the least but I finally figured out it was the gas valve stuck (I live at beach things rust fast) but the ac workied fine before the tech came out, I just turned it back on for the first time and everything cuts on and runs just fine for 2 or 3 minutes and then the blower stops blowing air through the air ducts/vents but everything else still runs fine the compressor outside fan just the blower stops, and it will only cut on after it has been switched off for 30 minutes or so and it will work again for a couple of minutes on initial start up what could it be, someone please help.
    Thank You,
    Vance
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    May 4, 2012, 07:14 PM
    To me it sounds like you have a bad run capacitor(cheap part) or a motor over heating and shuting down(not so cheap).
    vdubya420's Avatar
    vdubya420 Posts: 2, Reputation: 1
    New Member
     
    #3

    May 4, 2012, 09:58 PM
    Is that capacitor the one that the low voltage fan wire connects to, square has about 6 male contacts on it that the wires plug on to? Also ,where is the actual squirrel cage blower fan located at?

    Thanks so much fr your help.
    vdubya420's Avatar
    vdubya420 Posts: 2, Reputation: 1
    New Member
     
    #4

    May 4, 2012, 10:01 PM
    Thank you,where is the squirrel cage fan blower located at? And is the capacitor the small square that has the low voltage wire connected to it, it has about 5 or 6 male wire connectors on it for the female wire clasp to connect to. Thanks so much Vance

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a Frigidaire gas furnace which fires up for a couple of seconds then gas shuts [ 1 Answers ]

My Frigidaire gas furnace has 3 burners that ignite for a couple of seconds then shuts off. The electric ignition and fan works fine, it's just the burners that turns off after a few seconds. If I try turning the furnace on and off a few times it sometimes fires up and stays on. I have tried...

I have a Frigidaire gas furnace which fires up for a couple of seconds then gas shuts [ 0 Answers ]

My Frigidaire gas furnace has 3 burners that ignite for a couple of seconds then shuts off. The electric ignition and fan works fine, it just the burners that turns off. If I try turning the furnace on and off a few times it sometimes fires up and stays on.

Lennox gas pack. Heat chamber heats but blower doesn't come on. [ 8 Answers ]

Lennox gas back ignites but blower doesn't come on. Replaced wall thermostat and blower came on briefly but did not satisfy set temp.

Rheem Gas pack unit is blowing cold air [ 1 Answers ]

I have a Rheem Gas Pack. When the heat is turned on it isn't hot. More like cool air. On the outside of the unit you can feel the heat and hear it blowing on the inside. What could be causing this problem for the heat not to be coming out on the inside?

Trane Gas Pack Shuts Off Until Breaker Reset. [ 2 Answers ]

All, I have a Trane gas pack (AC and propane heat) that is approximately six years old. I awoke this morning to a cold house. Everything seemed okay on the thermostat, so I checked the house breaker. The house breaker had not tripped, but resetting the breaker enabled to the furnace to start and...


View more questions Search