    I have to feed a pump it has a load of 30 amps, is 115 volts and is located 1300 feet.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jan 10, 2012, 08:30 PM
    You have not given us all the info we would need to be accurate by try this calculator for yourself. Voltage Drop Calculator 2 awg aluminium would give you about a 9% drop in voltage.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jan 11, 2012, 05:29 AM
    I am not sure how Ballenger came up with 9% Vd with #2 Al.

    Using the same calculator I arrive at 17.7 % Vd using #2 Al at 120 volts, 30 amp load, 1300 feet.

    Recommended voltage drop is 3%, and I arrive at needing 1000 MCM Al wire ,using this calculator:

    Voltage Drop Calculator

    In any case, you need to look into using transformers at both ends to step up to a higher voltage at the feed end and as tep down transformer at the load end.

    Trying to deliver 120 volts 1300 feet is not practical.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Voltage Drop [ 3 Answers ]

I am trying to illuminate a tunnel about 3000' long temporarily with 9- 400 Watt Metal Halide fixtures spaced about 320' apart. I have a 120/240 generator single phase that I will use to back feed a 240/480 volt transformer to deliver 480 volts, single phase to the tunnel lights. At 480 volts I...

Voltage drop [ 1 Answers ]

The Voltage will drop after 150 meter wire ,how to sole the problem . Thanks to all

Voltage drop [ 4 Answers ]

A 300sq mm cable is to be laid for 600mtr. Distance. As the distance is large so there are considerable voltage drop at the receiving side. How can we cope up with this voltage drop at the receiving end? We want a constant voltage ofd 415 V at receiving end irrespective of input voltage? ...

Voltage Drop [ 2 Answers ]

I have a 20 amp breaker;there are a total of 7 receptacles on this circuit with a 15 amp GFI on the first receptacle. The first 5 receptacles in line work fine, the last two receptacles which are approximately 70 feet from the 5th receptacle flip the 15 amp GFI off when plugging in a drill. I...

Voltage drop [ 2 Answers ]

How far can you run an electrical cord, that is plugged into a 20 amp circuit, and still run a circular saw? If the saw starts slowly, will that harm the saw?


View more questions Search