    New goodman furnace won't light?
    Installed new goodman furnace. Blower turns on, igniter comes on, but no ignition. Gas is to the regulator, LP gas; switched jets, put silver springs in, set turns on lo-hi at 8 turns and 12 turns. Any suggestions?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Dec 28, 2011, 05:02 PM
    Is it a honeywell, or white rodgers gas valve. Either way, the settings in the conversion instructions for how far to screw in the springs is just for getting somewhat close on pressures. I have found that many times, they are way off. You need to have a monometer to actually check and adjust the high and low pressure exactly. If they are far enough off, it will not light.

    Also, and this is very important, did you fill the external trap with water? If not, the combustion air pressure switch may not close. The exhaust pressure switch will close, allowing the glow plug to ignite, but the if the other pressure switch doesn't close, it won't allow the gas valve to open. Simply dump water in the grey trap that is mounted to the side of the furnace, and see if it lites up. Im betting it will, unless of course the gas pressures are way off. Let me know. I am pretty familiar with newer Goodmans, so hopefully we can get this cleared up. Also, can you let me know the model number of the unit?

    Can you post some pics of your installation, including wiring, vent and combustion air piping, and drain setup. With enough pics, I should be able to pick out any install problems, if there are any. Take care, and good luck.
    johnn1954's Avatar
    johnn1954 Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 28, 2011, 06:15 PM
    White rogers valve. My gut tells me you hit the nail on the head with the drain hook up. I did NOT do that. Model GMH95/GCH95/GCH9. I do not have a monometer. Can I turn the low in to like 6, then back it out until I get a good flame? Likewise on the hi setting?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Dec 28, 2011, 06:32 PM
    Well, judging the flame by looks is really just a guessing game, so I can't really say for sure on that one. If you are just looking to get by, I would set the dip switch on the board to 1 stage, and let it burn if its burnign with a blue flame. Actually on the white rodgers, you can pretty much screw the high side in all the way and then back it out just a half turn and that gets you really close. Low side takes some fine tuning. Did putting water in the trap make the furnace fire?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman propane furnace won't light. [ 0 Answers ]

My Goodman furnace won't light after working fine after I cleaned the burners. Poor thing sat about 4 years without use. I just switched propane tanks and used the same tank as I had before and now it won't light. ED

Goodman furnace will not light, 2 flash LED [ 5 Answers ]

Hi, my name is mo from Arizona, my Goodman Model PGB furnace would not light. Pulled out the spark ignitor, flame sensor, ckecked voltage at gas valve, pulled out fuse, all of these parts looked and checked out OK. Turned the power on and the furnace worked fine. Remembering the LED was blinking...

Goodman pilot light on but furnace burners will not come on? [ 4 Answers ]

We have a Goodman furance that will not produce heat. The pilot light is on, the gas is released, but the burners will not kick in. Do you have any idea what is causing this problem.:confused: Scott's Chicago

Goodman Furnace - Won't Light, No Codes [ 3 Answers ]

Eleven year old Goodman gas furnace. The main vent blower will start, but that's where things end. The draft inducer motor doesn't start and nothing else in the chain obviously happens after that. The LED on the board stays red and never flashes any codes. I checked the voltage coming into...


View more questions Search