    Goodman furnaces troubleshooting?
    I put in the furnace and a/c myself . When I turn on the thermostat it gurgles at the furnace for a while takes like five to fifteen min to light up and blow is this the norm thanks gary!
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Nov 19, 2011, 03:24 PM
    Sounds like you may have water in the vent or supply line, depending on the heater, and the inducer fan is blowing through the water. Too much backpressure and the heater will not start. If it is a 90%, it will have plastic supply and vent. Pipes should not have any bow and slope to the outside. This is a fairly common callback if the lines are not sloped properly.
    hotironam's Avatar
    hotironam Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 19, 2011, 04:49 PM
    I was checking it out .the light was flashing 3 so the guide said it was the psi switch so I tested that it was good then I got your e mail and I checked the pitch and there was a bow in it and I could here water so I drilled a little whole there and a half of bucket of water came out so I cut the pipes made the pitch right and yahooooooooo thank you so much it works real good now thank you I owe you big time.gary w marchand
    skeeterlady's Avatar
    skeeterlady Posts: 1, Reputation: 1
    New Member
     
    #4

    Jan 22, 2012, 02:49 PM
    I had a goodman installed about 9yrs ago and every yr on the coldest days it will not start. The fan comes on but when it tries to light it just won't. I have had everything in it changed and after a bill for a thousand dollars it still does the same thing. This has been going on every yr since it was installed. I am a single mom and I hate this machine and I would never recommend this to anyone. Any ideas for a fix and has anyone else had these problems.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heil furnaces troubleshooting? [ 0 Answers ]

Blower kicks on ignighter come on late and explodes

Troubleshooting control boards for goodman furnaces [ 0 Answers ]

I posted question earlier,more info if needed, the furnace will fire up and run fine,but nothing happens in cooling mode.

Troubleshooting control boards for goodman furnaces [ 0 Answers ]

Unit runs fine for 3-7 days, then screen on digital thermostat goes blank and unit shuts off for about another 5 days,then all of sudden unit runs fine,problem not batteries for thermostat! When unit stops there's no power to thermostat, sounds like control board problem,have anyone heard of this...

Goodman furnaces troubleshooting [ 1 Answers ]

After 4 or 5 cycles the exhaust fan will come on as normal for about 1 minute and the burners will go out. The exhaust fsan will continue to run for 2 or 3 minutes then the inside circulation fan comes on with heated air and a very strong hot metal smell. What is the problem?


View more questions Search